i have 7 + 6, the 6 is 4 south with 2 of the east.

smaller string is set to 120 startup.

no figuired that one myself after reading the manual and checking the invertor settings.

my generation outputs are on pvoutput. Andy1.
you can see from the summer graphs how the early morning sun is affected and then how ouput is lowering after midday.
 
reply #13.
yes the 4 south with the 2 east does greatly effect my output hence the "looking at solaredge optimisers"

- - - Updated - - -

reply #14.
power one optimisers £££££
 
Dodgy system design. The split orientations will drag each other down - that will be the main reason it's underperforming. I would recommend getting the installer back to redesign the whole lot. Probably need to get on roof and re-connect several of the panels. Get them to downsize the inverter at the same time.
 
I think you can do a 9+4 arrangement with the 3.0: Inverter utilization ratio:87.3%

With the 3.6 you have: Inverter utilization ratio:73.6%
 
great example of my early morning losses is 04/05/11 on pvoutput. Andy1

shows the early morning shading then the quick tail off of generation after midday.
 
would rather change the layout myself.
have scaffold tower, roof ladders and by now the knowledge.
 
I would be seriously careful about changing an existing set up, I helped my company put a wind turbine through the MCS scheme ( which all products have to have in order to be eligible for FiT) and they were very clear that the product tested and its set up is what is eligible. For example your panels and the inverters (including how the inverters set up) must be the same as what was tested for the MCS certificate. Thus any change to the set up is not eliagble for the FIT as it is not what was tested.

Best option here is to talk to your installer of the product and see what options they have, as the panels MAY be able to be used with other parts without affecting eligibility of the FIT. As I'm sure you know, if you lose your FiT you will lose a lot of money!
 
thanks for all your inputs.

power optimisers behind panels with original invertor sounds a good bet?
 
1) Your PVI-3.6-TL-OUTD Inverter is larger than it needs to be for your present setup.
2) If your Romag panels are Vmpp 30.6V per panel > 7 East facing = 214.2 V, 2 East + 4 South = 183.6V.
3) The voltages on each of your strings are operational but not optimum.
4) Putting 2 East with 4 South will reduce the amount you can generate on the 2nd string.
5) It would be benefitial to have 9 East facing panels connected to 1 string, but what would you do with the 4 south facing panels you've currently got, their voltage wouldnt be high enough for the 2nd string on a PVI-3.6-TL-OUTD ?
6) Aurora Optimisers may be benefitial, but at what price. What will you gain for your investment?
7) PVGIS indicates 9 East facing 235W panels in Durham (2.115 KWh) could generate 1400 KWh.
PVGIS Indicates 4 South facing panels 235W in Durham (0.94 KWh) could generate 784 KWh.
Thus 2184 KWh is the likely theoretical amount you'd expect to generate with a properly designed system.
8) Solar system design isn't always straightforward because of the roof types, spaces, orientations & inclinations installers have to work with.
9) Do I think the installer designed your system to its optimum, no?
10) How much could you gain by altering this system? 2184 KWh V 1815 KWh (17%)?
11) In reality solar optimisers are unlikely to generate what you'd expect because of the low combined south facing panel voltage, shading issues, greater efficiency losses etc.

If you had more roof space to install more south facing panels, you could seperate your East facing panels from your south onto individual strings with higher combined voltages that would improve things.
It may be best for you to accept what your generation is and be pragmatic about it.
Many people may generate more than you but how much of it do they productively use 33%?
How can you better utilise the energy you generate to exceed typical usage?
 
Last edited:
looking that way.

there maybe something around the corner.

will not stop looking for improvements.
 