Just wondered what you all think about one of the changes to the regs.
Having to install an earth rod when changing a consumer unit.
Having to install an earth rod when changing a consumer unit.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Changes are coming, what do you all think in the UK Electrical Forum area at ElectriciansForums.net
I was refering to using a ground rod NOT bonding !
How many electric cars need to climb 10 floors to be recharged?And if it's a 10th floor flat, what then?
I more or less had to refuse exactly that request recently. It's going to get more common, and especially with hybrids which only need small charge off 13A socket, hard to draw a line against the regs.Potential Customer has asked me to put a power socket on the outside wall of his garage, what's it for I ask conversationally "its to charge up my hybrid"... PME, so IET Code of practice recommends min 2 by 2.4m rods. Plus get it back to MET. I wish I'd just shut up.
.3, In situations where it is not practicable to install Earth electrodes and perhaps even in situations where it is practicable, should upfront RCD protection also be provided so as to disconnect the supply in the event of a supply Neutral fault?
No it would not be the property of the DNO, just as an upfront RCD for a TT Installation would not be the property of the DNO..
& This would need to be before MET then wouldn't it? - Thus the property of DNO ?
At present if there were a supply Neutral fault, the bonding and extraneous metal pipework would become the Neutral.Agree - If the neutral is lost surely we should isolate the installation not add rods so it can carry on in a busted condition ?
.No it would not be the property of the DNO, just as an upfront RCD for a TT Installation would not be the property of the DNO.