Does anybody here have issues with changing 12V lamps to GU10 LED lamps in the same fitting?

Obviously involves taking out the transformer, changing the lamp holder and putting the fitting back.

I only ask because:

a) The tin cans usually have a label that says 12V
b) The tin cans are not earthed - but there are plenty of 230V ones that aren't earthed as well.

Thoughts?
 
just do it. GU10 lampholders are class2 anyway. park the cpc with a block if there,s no 3rd terminal but make sure the cpc is continuous throughout the circuit.
 

I think that means you agree with Tel Richard?

Would you both really be happy using a metal fitting that isn't earthed? I've always taken out the the old 12V fittings and replaced with fittings that state 230V. I've done this for a few reasons:

1. It states 12V on it so that kind of makes me think dont use 230V in it.
2. It's metal, so should be earthed at 230V.
3. There isn't always somewhere on the old 12V fitting that you can attach the GU10 holder bracket to to keep the terminal block away from the fitting.
 
I think that means you agree with Tel Richard?

Would you both really be happy using a metal fitting that isn't earthed? I've always taken out the the old 12V fittings and replaced with fittings that state 230V. I've done this for a few reasons:

1. It states 12V on it so that kind of makes me think dont use 230V in it.
2. It's metal, so should be earthed at 230V.
3. There isn't always somewhere on the old 12V fitting that you can attach the GU10 holder bracket to to keep the terminal block away from the fitting.

No. 2 not correct, no requirement to provide an earth if metal. Class 2 fittings can be constructed of metal and would not need an earth
No. 3 the gu10 lamp holders I buy from Eddys all come with a metal bracket which secures to the light fitting spring

I am doing a job next week which is exactly this scenario, also none of the fittings are fire rated either [emoji50]
 
No. 2 not correct, no requirement to provide an earth if metal. Class 2 fittings can be constructed of metal and would not need an earth
No. 3 the gu10 lamp holders I buy from Eddys all come with a metal bracket which secures to the light fitting spring

I am doing a job next week which is exactly this scenario, also none of the fittings are fire rated either [emoji50]

Yeah, but to be Class 2, it's got to have been assessed as Class 2 and carry the double insulated symbol.....if the OP's lights carry this, he's good to go; if not, he could carry on, but he would be taking a risk that I certainly wouldn't!
 
No. 2 not correct, no requirement to provide an earth if metal. Class 2 fittings can be constructed of metal and would not need an earth
No. 3 the gu10 lamp holders I buy from Eddys all come with a metal bracket which secures to the light fitting spring

I am doing a job next week which is exactly this scenario, also none of the fittings are fire rated either [emoji50]

Yes, thats quite right, but they would be classed as class 2 and have the correct double square sign. These will not be classed as class 2. With your above argument we could just say that we never have to earth any metal.


... you beat me to it Polo :smile5:
 
Last edited:
Aren't you altering the design of the lamp if you do what the OP suggests? Therefore you come responsible for the design and then need all the Risk Assessments and other paper work doing for it?
(Not very well put by me, but you get the gist of what I'm trying to say.... Hopefully...)
 
Aren't you altering the design of the lamp if you do what the OP suggests? Therefore you come responsible for the design and then need all the Risk Assessments and other paper work doing for it?
(Not very well put by me, but you get the gist of what I'm trying to say.... Hopefully...)

More than likely and probably need to be CE marked and all the rest of it. Yeah should change the fittings completely but it's minimal risk in my opinion so I'm happy to get paid
 
I have just suggested this option to a customer and did not worry at all.
They are marked 12V because we apparently need warnings not to use 230V on a specific 12V fitting.
I would class the assembly relevant to the lamp as the lamp holder as this is the only part in contact with the power supply.
The can is only in contact with sleeved cables and since the GU10 lampholder itself is classed as Class II putting in a metal box does not change this.

However I do also definitely see where you are coming from in terms of modifying a piece of electrical equipment and possibly increasing risk, but as gnselectricals says the risk is minimal in my view.
 

Reply to Changing 12V Downlights to GU10 LEDs in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
775
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
783

Similar threads

I'm not sure on the environmental implications, a good quality integrated fitting will last many years and be more energy efficient than the GU10...
    • Like
Replies
13
Views
1K
davesparks
D
Hi all, I have a couple of questions I'm hoping you can help with. I have put a solar panel on my kids play house which charges a 12v battery. I...
Replies
0
Views
360

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top