Since when has it been a "requirement" to do a test and inspection before a cons unit change ?

Is this by any chance Niceic reg making doctrine rearing its head again?

Also what are these pass and fail certs or notices or whatever else they may be called
 
Last edited:
[h=1]The new Electrical Installation condition Report which replaced the old periodic inspection report as of January this year. These certificates make provision for aspects of an installation to be classed as unsatisfactory or satisfactory. the new classification system of c1, 2 or 3 are applied c1 being danger present c2 potentially dangerous and c3 requires improvement.[/h]
 
Many schemes and publications "recommend" carrying out an EICR before changing a CU so that any problems are flagged-up before the change goes ahead for the very reasons that this post has highlighted.
That said, most electricians will check bonding, have a quick look around and do a 250v insulation test to give some idea of whether the shiny new RCD's are gonna trip.
 
Just to repeat what I asked earlier
Since when has it been a "requirement" to do a test and inspection before a cons unit change ?
 
Test first, then change CU if good, that makes sense.

I visually checked the bonding (10mm) when i quoted and also tested before CU change.

I disconnected the immersion when i IR tested the circuit with the immersion on it and still go 0M, so that needs to be further investigation

The guy just wants to know what needs to be done, he is ok with fixing what needs doing.

I will give him the news tomorrow

That's new info. It wasn;t in your op. How does the RCD in the new board stay on if this circuit has 0Mohm IR?
 
I was under the impression that the Installation Cert is for the work that you have carried out ie changed the CU, if he doesnt want the remedial work doing is there any problem just noting that on the cert?
 
That's new info. It wasn;t in your op. How does the RCD in the new board stay on if this circuit has 0Mohm IR?

I think there is a load somewhere that we couldnt find (something hidden). A sparky I know once spent a whole day trying to find a similar load and it turned out to be a socket plugged in a wall that had been plasterboarded over, i hope it isnt this bad. Anyway this circuit will need investigating. The owner has only lived in the place a couple of months so there may be something he/we couldnt find by looking
 
remember that I/R ing an existing installation is fraught with dangers, the neon on the switch fuse spur, the capaciter in that bathroom light fitting, the transformer still left plugged in behind the book case, all sent to confuse and give odd readings.
I know a bloke who wrote off the electronics on an expensive stair lift because it was still connected and he i/r'ed 500V between L and N.
 
You need to start doing some investigation work now on the cct that is giving you a reading of 0 Meg when IR tested.

As has already been said if you did have a dead short the ocpd would not hold so its likely that a load is still connected.

Start testing by useing your meter on low ohms and see what reading you get. If it is a radial cct it should not take you long to find out roughly where the load is looking at the readings that you get!
 

Reply to Changing a CU in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
814
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
873

Similar threads

That's a hell of a big jump to make, an RCD trips therefore a rewire is required! If a wheel on your van gets a puncture do you go out and buy a...
Replies
6
Views
987
davesparks
D
  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top