Checking a borrowed neutral | Page 3 | on ElectriciansForums

Discuss Checking a borrowed neutral in the UK Electrical Forum area at ElectriciansForums.net

loz

-
Joined
Jun 4, 2011
Messages
48
Reaction score
20
changing a fuse board today, house wired in the 60s with the landing light on the ground floor lighting circuit.
Tested at 250v ins res between the neutral of the 1st floor lights and the neutral of the ground floor lights. Result was 0.04meg ohm. Flick switch for landing light and the reading jumps to >200meg ohm.

Am I right in my thinking that this is a borrowed neutral?
In my head I can see the test voltage going up the upstairs lighting neutral, through athe landing lamp, down the live through a lamp one the ground floor circuit then returning back down the ground floor neutral
 
So Loz is the problem clear to you now. This situation often occurs with the landing light and often that part of the circuit is wired using pvc/ pvc singles.
fortunately, there's not so many singles seen these days. i put that down to the likes of eHarmony, match, elite, and all the other internet dating sites. gives credence to the saying " a dog is not just for christmas". :mad:
 
So Loz is the problem clear to you now. This situation often occurs with the landing light and often that part of the circuit is wired using pvc/ pvc singles.
Yeah crystal clear, I had it in my head, just needed a bit of confirmation on proving the fault, before powering the board up, which I had done but wasn't confident in myself. One thing I have learned is that things are so much clearer once it's drawn down on paper.
Both lights have been put on one mob for the weekend and I'm booked in on Monday to put a permenant live into the landing rose as well as a new switch drop and a 3 core downstairs to reinstate the 2 way switching correctly and enable me to split the circuits onto separate rcds. Shame it will be trunking drops but hey ho, can't win them all.
Thank you for your help
 
fortunately, there's not so many singles seen these days. i put that down to the likes of eHarmony, match, elite, and all the other internet dating sites. gives credence to the saying " a dog is not just for christmas". :mad:
Plenty of fish every time. I'm happy with my dog for life, wouldn't mind the mrs just for Christmas though
 
...and to lighten things further,it is a little known fact,that most hallways and landings,have multiple singles in them...just usually during a party :confused:
 

Reply to Checking a borrowed neutral in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
971
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
And exciting when that Hager AFDD finally tripped 😂
2
Replies
28
Views
2K
nicebutdim
N
Ok, please be aware that I am a 'do-it-yourself-er,' so if this isn't the right place to be posting this thread, let me know where I should be...
Replies
0
Views
457

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top