Hi, for a single phase LV installation, how do you determine whether to use 450V/750V or 0.6/1kV cable. Thanks
 
Last edited:
you select cable so as the rated voltage is higher than the actual voltage of the installation. no point in using 1kV rated cable on a 415/240V installation when 450V rated is compliant.
 
Also you might find that certain styles of cable are only available in the higher voltage rating.

There is nothing wrong with using the higher rating as such, but it can cost more and lead to larger cables to wrangle.
 
you select cable so as the rated voltage is higher than the actual voltage of the installation. no point in using 1kV rated cable on a 415/240V installation when 450V rated is compliant.

I agree, it seems obvious and yet much of the cable sold installed in Australia is 0.6/1kV. I'm trying to understand why this when 450/750 appears suitable?
 
A mechanically robust cable will usually have thicker, stronger insulation than a lightweight one, which allows it to be rated for higher voltages. There would be no point marketing a range of similar cables rated only for the lower voltage range, as the saving in material that could be achieved without diminishing the general capabilities of the cable would be minimal. OTOH Where small size and low cost are important the insulation is reduced and the voltage rating must be lowered to suit.
 

Reply to choosing cable voltage rating in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
268
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
755

Similar threads

I can imagine it just disappearing (loudly) under short circuit conditions, then the resulting blast/plasma etc. casing the busbars to flash over...
Replies
13
Views
695
Given that a lot of EV's only charge from one phase when connected to a 3 phase chargepoint does the customer really need a 3 phase chargepoint...
Replies
1
Views
602

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top