you select cable so as the rated voltage is higher than the actual voltage of the installation. no point in using 1kV rated cable on a 415/240V installation when 450V rated is compliant.
you select cable so as the rated voltage is higher than the actual voltage of the installation. no point in using 1kV rated cable on a 415/240V installation when 450V rated is compliant.
I agree, it seems obvious and yet much of the cable sold installed in Australia is 0.6/1kV. I'm trying to understand why this when 450/750 appears suitable?
A mechanically robust cable will usually have thicker, stronger insulation than a lightweight one, which allows it to be rated for higher voltages. There would be no point marketing a range of similar cables rated only for the lower voltage range, as the saving in material that could be achieved without diminishing the general capabilities of the cable would be minimal. OTOH Where small size and low cost are important the insulation is reduced and the voltage rating must be lowered to suit.