Circuit Breaker drops before Fuse | Page 2 | on ElectriciansForums
Discuss Circuit Breaker drops before Fuse in the The Welcome Forum area at ElectriciansForums.net
I would suggest you get a spark to test the resistance of the mut and the IR too ............ to begin with
Upping the MCB is not recommended ....
I've seen these 3kW items eat up the fused connection unit over time, but not so much the MCB. Inspection and test, and if no fault is found I'd replace the 16A MCB with a new one (exactly the same) as they're cheap and it may have just gone soft. It should never trip at 16A, let alone 13A.
Does your Consumer Unit have residual current detection -there will be a test button on it? Someone asked this question earlier and I think you may have missed it. If it does is the underfloor heating circuit breaker fed from it?
When you call in the electrician ask him to measure and record the current flow through the mat and the voltage of your mains supply at the same time.
Also ask him to check the tightness of all screws which connect the circuit breakers to the busbar - it may be that one or more adjacent mcbs are getting warm and the copper busbar being a good conductor of heat is allowing heat to flow to the UFH 16A mcb warming it up and making its thermal trip readier to trip at a lower current/after a shorter time interval.
Heat transfer can also occur between mcbs placed side by side - out of interest what mcbs are to the left and right of the UFH 16A mcb? I have come across a problem when a 6A mcb lighting circuit (passing 4-5 A) would trip in the evening - it was next to a 16Amcb for the immersion heater which was was on and young children were having their night time baths one after the other in fresh hot water. Separating these mcbs with a blank solved the problem.
Wilco: Just replacing the B16 MCB was my first impulse.
Marconi: Excellent ideas. The MCB is at the end of a row. To its left, the B32 MCB kitchen ring main (which carries a kettle, microwave and dishwasher as its max load) I'll talk to the electrician when he comes and ask him what you suggest.
Thanks for all your help, guys. I won't be able to do do any experiments this week or next, but I'll get back here when I can.
I'd recommend you don't do experiments but rather have this tested properly.
Its not uncommon for a fault in a heating element to only appear when it is hot and expansion has occurred.
I would probably start with measuring the cold resistance, cold and hot insulation resistance, running current and leakage current.
12 years doesn't sound like an unreasonable lifespan
It just needs 14A to blow the 13A fuse, leaving the 16 intact.
I’m afraid I do not agree with this, What many people may not realise is that a 13A rated fuse is not designed to actually blow at 13A. In fact a 13A fuse will allow a current of 20A to pass indefinitely without blowing. If you look at the attached graph, it shows the operating characteristics for both 3A and 13A BS 1362 fuses. The grey shaded area is the point where the fuse is designed to operate. So for example, a 13A fuse will blow within 0.01 - 0.3 seconds for a fault current of 100A; shown in red on the graph. For a current of 20A, shown in blue on the graph, a 13A fuse will not blow!
So that is the reason the 16A MCB will trip way before the fuse does.
I would disconnect the heater mat and measure the resistance as a starting point, this should be somewhere between 17 & 18 ohms for a 3kw mat rated at 230v.
Then carry out an IR test on the mat.
The heater mat will pull a little more current when first switched on (usually around 10%) so this is getting a little close to the 16A rating of the breaker.
If the mat tests out ok, I think I would change the breaker as it has probably fatigued over the time it has been installed
#23 and #24
If you read the thread on a bit, I say I misread the OP, so my initial reply was mostly in error.
The part about 13A, 14A and 16A... was an attempt to explain electrical loads and overcurrent protection in laymans terms to non professionals that might be reading.
Everybody is quite right in saying the 16A breaker will trip before the 13A fuse knows there's a problem
Reply to Circuit Breaker drops before Fuse in the The Welcome Forum area at ElectriciansForums.net
It sounds like there is damage to the wiring underground. Do you know what kind of cable was used, in any underground wiring is used has to be UF...