steve snakeman
Ive just finished testing a small domestic board.Everything fine untill I test the lighting circuits.Readings are as follows
R1+R2 0.89
Insulation resistance >299
Polarity OK
Earth continuity OK
These readings are for the first lighting circuit,the second circuit was similar.
so far so good,however when I come to do an earth fault loop impedence test(Zs)the test starts off ok but then the circuit breaker switches off after a few seconds(not the RCD).I move to the second lighting circuit and the same thing happens.I have removed all the pendant covers and switches and can find nothing wrong anywhere .....why is this happening???
R1+R2 0.89
Insulation resistance >299
Polarity OK
Earth continuity OK
These readings are for the first lighting circuit,the second circuit was similar.
so far so good,however when I come to do an earth fault loop impedence test(Zs)the test starts off ok but then the circuit breaker switches off after a few seconds(not the RCD).I move to the second lighting circuit and the same thing happens.I have removed all the pendant covers and switches and can find nothing wrong anywhere .....why is this happening???