Ive just finished testing a small domestic board.Everything fine untill I test the lighting circuits.Readings are as follows

R1+R2 0.89
Insulation resistance >299
Polarity OK
Earth continuity OK

These readings are for the first lighting circuit,the second circuit was similar.

so far so good,however when I come to do an earth fault loop impedence test(Zs)the test starts off ok but then the circuit breaker switches off after a few seconds(not the RCD).I move to the second lighting circuit and the same thing happens.I have removed all the pendant covers and switches and can find nothing wrong anywhere .....why is this happening???
 
When you do an Earth loop test it pushes about 20A down the circuit, most of the time 6A MCB's can handle this but sometimes they trip. link across a couple of mcbs to do the test (single phase only) or move the circuit to a higher rating for the test.
 
Last edited by a moderator:
I have no idea if what I'm about to say is true, but I have just read that when performing an Earth Loop test a 25A pulse is used during the test, although only for a short period of time, it can cause some MCB's to trip.

Again, its only what I've read.
 
thanks guys,what you are saying appears to be true but this is the first time it has happened to me in ten years lol. This however appears to be plaussible .I will try again in the morning and let you know :)
 
thanks guys,what you are saying appears to be true but this is the first time it has happened to me in ten years lol. This however appears to be plaussible .I will try again in the morning and let you know :)

Cant believe you've been testing for 10 years and not had 6a type B's trip on a Zs test....It's VERY common.
 
It is true but really you shouldn't ever bypass the circuit breaker but calculate your Zs instead.​


Or, open the MCB, join L to E at the furthest point, do the test across the open MCB​
 
ok Guys, but I was taught that we should not be using a live earth loop test on lighting circuits, but should measure R1+R2 and add to Ze to give Zs, i.e. avoid live testing except where it's essential, eg for Ze.
 
ok Guys, but I was taught that we should not be using a live earth loop test on lighting circuits, but should measure R1+R2 and add to Ze to give Zs, i.e. avoid live testing except where it's essential, eg for Ze.


You've already been told, that's a load of crap, when you're talking about testing procedures...
 

Reply to circuit breakers going off?? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Ok, please be aware that I am a 'do-it-yourself-er,' so if this isn't the right place to be posting this thread, let me know where I should be...
Replies
0
Views
455
Check the clearance between the back panel and/or terminal cover that you've removed. Look for small burn marks.
Replies
3
Views
499

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top