I have a question i hope someone can just give me a little clarification on .
When carrying out preliminary cable design for a given circuit we use this formula = ( milliohms per metre x Length x multiplier Factor for maximum operating temperature ).


Do we still need to use the the maximum operating temperature factor for the given cable type in the above formula if we use the Zs measured value (the 80% rule ) against the protective device .


example
A Radial circuit is wired in 2.5mm 1.5mm , the Length is 25M the Calculated value by design would be ( 19.51 x 25 x factor 1.2 ) divided by 1000 which would = ( R1+R2) as 0.58 Ohms obviously add this value to the Ze and then check against the protective device Zs measured value ( 80% rule ) to confirm is this value complies .


or would we just use the formula this way ( 19.51 x 25 ) divided by 1000 = ( R1+R2 ) = 0.48 ohms added this value to the Ze then check against the Zs measured value of the protective device .

Do we still use table I1 from the on site guide page 220 when calculating by design the R1+R2 or is this not used because of the 80% rule applied to protective devices Zs .
 

Reply to Circuit design calculation in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
A combination of all. Here's how I look at it: A supply voltage of 216V (lower limit that is permitted to be supplied) supplying a circuit with...
2
Replies
31
Views
2K
  • Question
(2.4-0.4)×1.2+0.4 = 2.8ohms
Replies
4
Views
1K
Hi David. I'm currently doing this same design project from home. Can I ask you a question? When working out the design current for the circuits...
Replies
4
Views
3K
  • Question
Read up on the definitions of conductors, then circuits. Then double check what bunching is defined as - and the answer will be apparent PLUS...
Replies
1
Views
2K
  • Question
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks