Guest viewing is limited
Hi Guys,

I'm currently designing an installation that will be used to configure multiple pieces of electronic equipment such as PC's, Servers, All in ones etc. Its going to be set up in bays such as the picture attached. With it being a full socket installation I was hoping for some guidance if I'm approaching the maximum demand calculations correctly with diversity. There are a lot of circuits as there will be a high amount of earth leakage from the equipment being used and IET suggesting to keep it less than 30% of the 30mA. I've attached a screenshot of the equipment being used. There is a possibility that all bays will be used at the same time with all the equipment plugged in and going. Any suggestions would be great. Thanks.

Screenshot 2024-12-11 at 19.28.28.png
Screenshot 2024-12-11 at 19.34.34.png
 
have you considered using rcd sockets?
that way you don't have to worry about cumulative earth leakage tripping rcd's
a faulty device wont take out all the others on test.

you may consider wiring the earth as a ring, even for radial circuits to ensure you have a robust system for dealing with high leakage currents.
 
have you considered using rcd sockets?
that way you don't have to worry about cumulative earth leakage tripping rcd's
a faulty device wont take out all the others on test.

you may consider wiring the earth as a ring, even for radial circuits to ensure you have a robust system for dealing with high leakage currents.
Cheers for the reply James.
It did pass my mind but because it is a power circuit less than 32a doesn't the cable supplying the sockets have to be rcd protected as well? Regarding the high integrity earthing, the way it is designed at the moment is less than 10mA and the spec of future configurations will not be near that either so I believe it isn't required? It's more the diversity calculations and max demand I could do with a hand on, just to make sure I'm definetly doing it correctly.
 
In the U.K., depending on cable type and routing, an rcd may not be required
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
cheshire

Thread Information

Title
Circuit design for computer circuits.
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3
Unsolved
--

Advert

Thread statistics

Created
Brownie,
Last reply from
James,
Replies
3
Views
302

Advert

Back
Top