Is there a problem testing a circuit if there is a SELV spur off the circuit?

eg, doorbell, power shower..

Thanks
hmiddity
 
Yes certainly on an IR test as it would give you a dead short if you do not disconnect the appliance. If you can not disconnect the appliance you can test as per regulation 612.3.2 as L/N joined to Earth.

On a R1 + R2 then no, as the system will be isolated and you will be testing before the load side of the appliance. If it was a live Zs test the same it would be done on the supply side of the system.
 
Not really a problem.
The feed circuit would be tested as normal at 500V DC, and the SELV spur at 250V. You would then need to test the separation between the live conductors of the SELV spur and the feed circuit at 500V.
 
Yes certainly on an IR test as it would give you a dead short if you do not disconnect the appliance. If you can not disconnect the appliance you can test as per regulation 612.3.2 as L/N joined to Earth.

On a R1 + R2 then no, as the system will be isolated and you will be testing before the load side of the appliance. If it was a live Zs test the same it would be done on the supply side of the system.

Thanks Malcolm. when you say disconnect would it be ok just to remove the fuse from the fused spur or should the cables to the transformer be totally removed?
I was reading the User guide (probably 612) which mentioned the L/N join.
I had an electrician in to check the wiring (35 years + and part P) but he didn't seem to think that it would be a problem.
regards HMIDDITY
 
Certainly false reading would be given on an IR test. Pull the fuse and disconnect the neutral.
Hmm no problem eh? Wonder if he'd be saying that when he gets a 0 reading he can't figure out.
 
Hello Malcolm,
The spur is a double pole fused switch with the feed taken from the lighting circuit.
So if the switch is off will it be ok to run the tests on the lighting circuit?
One other silly question, if a lighting circuit is said to be 'open' does that mean the light is on?
Regards and thanks for your time.
 

Reply to circuit testing in the Talk Electrician area at ElectriciansForums.net

Similar Threads

Given the apparent lack of earth, combined with no short circuit or over current protection, I'd contend that luck has been the sole factor...
Replies
5
Views
431
nicebutdim
N
Because of the addition of separate columns for RCD type etc. I use Easycert software which gives the option of fitting it all onto one page.
Replies
1
Views
281
loz2754
L
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
1K
Not all sockets isolate both the live and neutral when you turn the switch off Many just isolate the live leaving the N connected. So the...
Replies
1
Views
230
Ok, please be aware that I am a 'do-it-yourself-er,' so if this isn't the right place to be posting this thread, let me know where I should be...
Replies
0
Views
359

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks