Hi guys, after flat bashing for years, I'm now on my own and seem to only be working on TT installations. Can someone just clear this up for me please?When installing a new cu in a TT installation, do I need a 100mA time delayed main switch or can I just put a normal main switch in and have a split 30mA board.Steve
 
Aargh!

Where is it leading??? You can't leave us hanging like this. I've never heard of double and single pole RCBOs - and now I'm thinking ***t did I install the right one last week!!

It's a just a joke, right?
 
The reg's call for isolation on all live conductors on a TT system but as pointed out in Guidance Note 5, a double pole main switch is acceptable (4-pole on 3-phase & neutral supplies).
 
Because of the nature of a TT system and the instability of a reliable earth, N-E fauts can sometimes not be cleared. The use of double pole protection devices should be used and though the regs fall short on this IMO I always would fit a double pole RCD, which was done as an upfront ELCB and then RCD.

This is what was always done pre RCBO days and I think that the IET have not moved with the advent of single pole RCBO's when using them on TT systems .

Which is why I asked if you are fitting a main double pole switch you will conform to Reg 537.1.2, but if only single pole RCBOs are fitted, I would consider that less than safe.
 
you wouldnd need both id go for an 80amp RCD main switch which is double pole no need for the main switch then dont forget the 63/80/100 RCD is not an overload device but an isolator/RCD the current rating on them is what they can handle
 
you wouldnd need both id go for an 80amp RCD main switch which is double pole no need for the main switch then dont forget the 63/80/100 RCD is not an overload device but an isolator/RCD the current rating on them is what they can handle

I understand that they provide no overload mate, so if I understand, RCD main then the 4 circuits....done and dusted?
 

Reply to clarification of cu upgrade on TT installation in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
920
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
956
  • Question
Good point, I was assuming an up-front RCD is for fault protection within DB, etc, and to cover for a failed RCBO for fault conditions, not as...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top