pushrod
Been asked to swap over a class 1 fitting for another old existing class 1 on a first floor hallway - however there is no cpc on the light circuit! (early 1960s house). In the loft there is a rfc junction box close at hand. What about putting a 4mm g/y single from the light fitting to the J.B. and a note and sticker on the CU to say what has been done.
Am i missing something obvious in the regs to say no - after all a light could be earthed by a ring main cpc if it was fitted via a 3A FCU. A rewire is out of the question and leaving it alone is no safer, although there are no simultaneously touchable earthed parts/ extraneous conductors.
cheers.