Cheers, a report been submitted to the Client & suggests improvement, with the first option to disconnect all Light Columns & hopefully IR measurements will improve.
Ok good luck with that Cliffed, but I perhaps misread or assumed the columns had been disconnected and like others assumed it was maybe a cable fault/low IR but now it could equally be within the column or one or more of the actual light fitting(s)?
 
As above. I assumed the cable had been isolated, and the poor readings were from that alone.
I almost expect to find less than perfect IR readings from any outdoor lamp fitting that has been in use for some time.
 
As above. I assumed the cable had been isolated, and the poor readings were from that alone.
I almost expect to find less than perfect IR readings from any outdoor lamp fitting that has been in use for some time.
The cable had been isolated & IR tests were performed & measurements were poor throughout.
Within the time we were on site it became clear that this was not a simple fix, & we were actually concerned that we may even make the situation worse, disconnecting & then reconnecting.
There’s approx 30 columns & access is not great, hopefully the Client will go with a complete disconnection & see where we go from there.
Cheers for your input everyone
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
IR External Car Park lighting
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
17

Advert

Thread statistics

Created
spraystone UK,
Last reply from
cliffed,
Replies
17
Views
945

Advert

Back
Top