Hey everyone.

Recently got called to a job where I needed to change over a light fitting and other small jobs. Upon testing the circuit no earth was present, I investigated the circuit thoroughly and gave the customer a few options on what to do. The customer decided to go ahead with changing all the light switches and light fittings to class 2. Fuseboard was also upgraded and earth bonding installed.

The job is now completed, I have printed out a label and left on the fuseboard mentioning about the lighting circuit has no earth.

Should I also fill out a risk assessment and print out and leave with the EIC at the fuseboard? ‘This is the first circuit I have installed class 2 items on so am a bit unsure,normally the customer gets it re-wired but on this occasion the customer didn’t want this carried out.
Attached is one I have filled out which I hope is correct.

Thanks for any advice given.
[ElectriciansForums.net] Class 2 advice needed please
 
What should I do with regards to the risk assessment? Should I or should I not fill one out? I feel like I need to list all items within the property changed and have them listed with the EIC to ensure any future electricians entering the property do not change them to class 1 items just to cover this situation as much as I possibly can.
 
What should I do with regards to the risk assessment? Should I or should I not fill one out?.

You must surely have assessed the risks before you started work, so why not just document this? You didn’t just make this departure from the regulations without careful thought and planning did you?

Have you recorded this in the departures box on the EIC?
 
Catalogue

Home > Industry Labels > Electrical Labels > Labels for BS7671

No Provision For Earth Labels / Missing Circuit Protective Conductor Labels
[ElectriciansForums.net] Class 2 advice needed please
Zoom
[ElectriciansForums.net] Class 2 advice needed please
[ElectriciansForums.net] Class 2 advice needed please

Our Price: £5.50(Exc. 20% VAT)(£6.60 Inc. VAT)
–+
<p><font class="subtext">(Details shown apply to the default selection)</font></p>
Choose Quantity:
Model: LP2082-50
Quantity: 50,100,250,500,1000
Size: 75mm x 50mm

(2 Reviews)


No Provision For Earth Labels/Missing Circuit Protective Conductor Labels
Size 75mm x 50mm

Material white vinyl

Adhesive Permanent


Additional Information
No Provision For Earth Labels (Also know as Missing Circuit Protective Conductor Labels) as Prescribed in BS7671 Requirements for Electrical Installations
 
This guy seems to be getting a lot of stick for basically making the best of a bad job?

However high and mighty we electricians might think we are, and however misguided customers may be, we can't force people to have work done if they don't want it!

The result in this scenario is an upgrade of CU, which will include 30ma additional protection, and the removal of metal accessories for plastic, which type tested or not, will be inherently safer.

End product is a safer installation, if an imperfect one. The other option is to keep going with the high and mighty act, and walk away potentially leaving 3036's and metal switches! I think I know which route I would take....
 
This guy seems to be getting a lot of stick for basically making the best of a bad job?

However high and mighty we electricians might think we are, and however misguided customers may be, we can't force people to have work done if they don't want it!

The result in this scenario is an upgrade of CU, which will include 30ma additional protection, and the removal of metal accessories for plastic, which type tested or not, will be inherently safer.

End product is a safer installation, if an imperfect one. The other option is to keep going with the high and mighty act, and walk away potentially leaving 3036's and metal switches! I think I know which route I would take....
I walk from jobs like this unless the client accepts any rewiring as necessary. You advise and if they decline, walk away.
 
All lights and switches without a earth present were changed to class 2 and all switches DO have screw caps fitted.

The customer had recently had all the rooms decorated and didn’t want any damage to be made to walls/ceilings so changing to class 2 was the only option.
I hope you are not stating you have fitted Class II switches because this is far from the case. Aside from the fact plate switches are not Class II the metal fixing screws require earthing and fitting plastic caps in no way provide any level of double insulation. A better option would have been Nylon screws.
 

Reply to Class 2 advice needed please in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Thanks for your reply. You are quite right, I’ve taken one down this morning and the cable is twin & earth but the earth has been cut right back...
Replies
2
Views
467
It applies to commercial if it shares the same supply as a dwelling.
Replies
4
Views
576

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top