The test will be carried out with the earth lead hovered around all the seams, switches and fixing areas.

It seems weird and takes a few repeat tests but it simulates the casing of the appliance being in contact with earth in the failure of the Class II insulation.

Precisely Widdler, but most testers, particularly non-electricians, seem to think a single test with the earth lead in contact with the case is OK, or as I witnessed last week at a local charity shop without the earth lead even attached to the PAT!
 
Yep Markie thats the point I was trying to put over that PAT guys and some electricians are plugging them in the tester with the earth lead on the floor "pushing" the button and hey its a pass without understanding the circuitry.

Plus the more I get into PAT the more I realize that there is a lot of people doing it with no basic understanding yet they are qualified to test and are convinced that if the tester says pass then thats ok isnt it ? Add this to the failure to check fuse ratings and flex condition and I am thinking what a con.

As I have said before this is not a lecture or a put down but I am speaking to people who have done this for years and still dont have a basic understanding mind if you can get qualified in 5 weeks with the schemies queing up to badge is it any wonder why our trade is seen as a joke
 
write to your local rag, saying for persons getting electrical work done , too check certificates with local colleges, but would local colleges reply to these requests , in a sense regulating electrical work...

its upto the customer to deem your competant.. its all a farce ....... no1 cares until someone is hurt..
 

Reply to Class II debate in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
771
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

  • Question
The symbol is from IEC 60417-5172-2003-02 and as far as I know showing the symbol is not mandatory (and I seem to recall that is stated in the 5th...
Replies
1
Views
426
  • Question
Hi. I recently bought an electrical ceramic heater which was described as class 2. Now I've opened the packaging, I can see that the rating plate...
Replies
0
Views
157

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top