Piratepete

Hi Guys
I have a Domestic Installation
One 14way CU with RCD Main Switch in meter cupboard
One 4way CU with RCD Main Switch in garage fed from above CU
One 8way CU in another part of the house fed from a Switch Fuse and RCD in the meter cupboard.

Wiring faults found. Codes required please!

1. Cutout fuse is 60Amp. So is the fuse in the switchfuse supplying the 8way CU! So no grading
2. 2 standard 30mA RCDs in series. No discrimination.
3. Lack of grommits in metal socket backboxes.
4. The supply to the Immersion Heater has been tapped off to supply sockets for Security cameras and also loft lighting. All subfused OK, but is it permitted?
5. No bonding to gas- that's a C2, isn't it.
6. Garage supply is 40Amp which I think is too large for the cable size/length. Exceeds volt drop.

Best Practice Guide No.4 only describes (5) above. :(
Looking forward to your replies.
Thanks
Pete
 
One 14way CU with RCD Main Switch in meter cupboard
C3 overall RCD applies
One 4way CU with RCD Main Switch in garage fed from above CU
C3
One 8way CU in another part of the house fed from a Switch Fuse and RCD in the meter cupboard.

C3
Wiring faults found. Codes required please!

1. Cutout fuse is 60Amp. So is the fuse in the switchfuse supplying the 8way CU! So no grading
....
2. 2 standard 30mA RCDs in series. No discrimination.
C3
3. Lack of grommits in metal socket backboxes.
C3
4. The supply to the Immersion Heater has been tapped off to supply sockets for Security cameras and also loft lighting. All subfused OK, but is it permitted?

NO CODE
5. No bonding to gas- that's a C2, isn't it.

C2
6. Garage supply is 40Amp which I think is too large for the cable size/length. Exceeds volt drop.

C2 depending on volt drop and cable size???


 
agree^^^ no.6 may not be a C2 if the actual load is low enough to comply with VD, and the OCPD is correctly sized for the cable feeding the sub-main.
 
nice to see a bit of unity!!!

and piratepete i always use common sense when doing codes...!! Will/Could it Kill some one... C1.... is it against Regs but kinda safe C2 ...... every thing else that you decide needs improving is a C3

or take the would you have it in your home approach!!
 
Thanks Durham Sparky.
I'm impressed! So the installation is 'Unsatisfactory' then. :drool5:
You've ducked fault (1). Any particular reason?
Regards
Pete
 
how long is the run between these 60A fuses? my opinion would be a code 3, as it;s not presenting a danger ( assuming that the feed to the sub-main is suitably sized for 60A OCPD
 
the OCPD is correctly sized for the cable feeding the sub-main.
A bit border line, this. Cable is 2 core 4mm SWA. I can't identify whether it's 70deg or 90deg. If 70deg, it's only good for 37 Amps. OCPD is 40Amps. However it's impossible to draw 37 Amps. Was XLPE cable around 22 years ago?
I think I'm being too picky!
Pete
 
end of the day every one has a differnet take on the regs and codes....

take down sockets fitted 1988 with no rcd for example!! code 1 or code 3..... i say 50/50 split would be the responses!
 
end of the day every one has a differnet take on the regs and codes....

take down sockets fitted 1988 with no rcd for example!! code 1 or code 3..... i say 50/50 split would be the responses!
C1 is for a real and immediate danger. if no live parts are exposed, then the lack of an RCD can only be a C3.
 

Reply to Classification Codes Required Please! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
936

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K
  • Question
Thank you, that's a really helpful post, nice & clearly stated and helps me clear up a lot of confusion on this matter.
2 3 4 5
Replies
65
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top