Client is being very naughty and im caught in the middle | on ElectriciansForums
Guest viewing is limited

Discuss Client is being very naughty and im caught in the middle in the UK Electrical Forum area at ElectriciansForums.net

Joined
Dec 24, 2016
Messages
404
Reaction score
92
Location
london
I carried out an EICR for a charity music school, the building is a small brick building with a few ring circuits and lighting circuits.
I am going to be upgrading a few consumer units.

I asked them where their meter was and they said they currently do not have one and do not intend to have one???
is this my problem as its not unsafe having a Henley block in place of the meter??
 
Good one... What the procedure if you see someone with 2 CU's and one has bypassed the meter, or along those lines...? You get the idea...
 
Is it definately a DNO incomer? On some multi-building sites, such as colleges and universitys, the distribution cabling was installed by the local electricity board with a central meter and customer switchgear. The submains look like DNO cables (paper insulated lead etc.) but are in fact private, being metered upstream.
 
I would probily let them off with it being a charity (would feel charitable), would tell the client that he needs to call and get a meter installed (which they probily wont) and then note on the certificate that "there is no meter and have informed client that he needs to call and get one fitted" and just leave it at that.
 
Effectively you are there to assess the safety of the electrical installation. There is no electrical hazard in being unmetered. An N/A would be applicable for the report.
You then have the dilemma of is this something I wish to report or do I check up to see if it legitimate or do I ignore it.
This is down to your level of energy, moral compass and interest.
 
The views on this is interesting to read.
We usually go on about doing a proper job and doing things by the book.. It sounds like that's ok ...as long as it's to our liking...
I suppose at the end of the day, as @Richard Burns says, it's down to our moral compass...
Personally I would question the set-up with the DNO.
 

Reply to Client is being very naughty and im caught in the middle in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
even allowing for diversity this sounds a bit tight for a 100 amp supply, can you tell us what the existing circuits actually have connected to...
Replies
2
Views
659
  • Question
Thanks for the replies, I appreciate it.
Replies
4
Views
604

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top