I have wired up a couple of remote switches for a three phase fan in a paint room, two switches by the door, one inside the room one outside, this so fan can be controlled when entering and leaving the room, i have wired these as a closed loop hold on circuit with momentary switches, my problem is that they also require the fan to run on for 15-30 mins, to clear the air at the end of jobs, I just cannot find the right type of relay/timer because it is a hold on contact, once the timer button is pressed i need it to maintain the contact for the period of time required, break the contact then once the coil has dropped out ,make the contact again, so the hold on loop is ready for the next operation, i thought i had cracked it, by feeding the coil from the common of a n/o , n/c timer switch, so the feed is looped through the n/o , n/c . then when the timer changes from one to the other the contact would be broken, works on paper but in practice it is to quick and the coil remains energized,.
I have tried RS , but cannot find what i want. Any help would be much appreciated.
 
ok , at the moment i have momentary on switch ( push to make )and momentary off switch, ( push to break ) these are manually operated, i then have another momentary on switch which will operate the timer circuit when it is installed,
 
What sort of paint is it? Some are highly flammable so the starter and P/B’s should be outside the storeroom.
I will do a drawing for you when you answer the question.
 
They have an existing spray booth within the room, this has been operational for a couple of years, the reason for the controls by the doors is that they were having problems with the negative air pressure, so every time they opened the door ( which was difficult in itself with the fan on ), all the crap from outside would fly in , ( up to now the controls were adjacent to the fan ) none of the electrical items, switches or light fittings are explosive resistant type, so i dont believe this to be an issue. I should tell you that the coil is 400volt type , with one side permanently connected to incoming phase, I have extended the other side of this to control the contactor , although this is obviously on a different phase
i am therefor only running 230 volts through control equipment,
 
jus a quickie of 2 play golf, can u put the stop ctrl thru a time delay off contact,via a c/o contact,this will then alow norm operation ,then when the time delay is needed,maybe via a push button,this brings in the timed contact.cheerio
 
Hope the golf was good,

... the time delay is the problem, everything else is wired and working, I need a timer which will open after a set period then close again, allowing the closed contact circuit to drop out, ready for the next time it is energised. I have tried a couple of changeover relays to do this but they do not open long enough for the circuit to be broken.
 
Im with tony on this one known of 2 explosions and 1 death resulting from spray paint rooms... you start by getting a COSHH on the paint or any other products used in the room to establish whether to walk away or tell the customer it needs a complete new system (expensive to say the least).

Ive got a very dark feeling about this job... intrinsically safe gear and/or remote operation, as goes your problem their are plenty of solutions from small plc program to having the start stop signal a timer relay that controls contactor coil, the stop signal would be the timer signal to time out. You can also get plc relays that can be programmed or set up to act or time to your needs.

Ill re-iterate my feelings though, because you have started this job you are wholely responsible for the existing regardless to its compliance or not before you got there, hope you can appreciate the hole you may be digging as its clear from reading you are not sure about the materials been used etc and the risks they pose.
 
Last edited by a moderator:
What if a situation arises when the fan needs to be stopped immediately?

Are these fans in paint booths desired to run-on in fire alarm situations?

Please excuse my naivety.
Its not usually employed in the codes of practice but common sense would denote that explosive gasses should be expelled with a fire alarm incident hence they should carry on running or be linked to fire alarm, i will stand corrected but believe its an oversight in fire safety at present.
 
Mmmmm, i did think long and hard about this one, alas not long enough or hard enough, as i am taking the control wiring from one phase to operate the 400v coil, using momentary switches, you are correct, at the moment of contact at the point of energising the coil , there would be 400 v at these switches/contacts. I have taken a neutral with the control circuit to allow for an indicator lamp and to operate timer, this is what i was referring to as 230v control circuit.........honest.
 
This is a good point,.... if i can just get the timer circuit up and running , i should be able to link in the fire alarm to allow a run on in the event of a fire. I shall bring this to their attention.
If i send them a communique explaining that i feel all electrical items should be intrinsically safe etc. within this area , will the responsibility pass back to them ??.
I,m off to look at plc relays.
 

Reply to closed circuit coil on 3 phase contactor needs to have time delayed off switch in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
290
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
276
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
354

Similar threads

You only need to switch the lines and the contactor is rated per pole so for example a 16A four pole contactor would be fine.
Replies
1
Views
231
Also use a tails gland and clamp if available and make sure tails are secured to a wall. The danger here is a live to earth fault in the Consumer Unit
Replies
7
Views
536

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top