Hi,
I have had PIR done on a flat that was built in 1991, I have had a code 2 on the lights in the bathroom not on an RCD even though it is an IP 56 fitting, is this correct? The maximum demand has also been put at 50KVA for a 2 bed flat...!

Thanks
 
code 4 for the bathroom lights, as long as there is no apparent danger. 50kVA is probably he meant 50A.
 
The bathroom should have either RCD protection on all circuits or supplementary bonding.

If SB is in place then lack of RCD = code 4

If no SB in place there should be two coded items:
No SB = code 2
No RCD = code 2

IMO

Has the supp bond box been ticked on the schedule?
 
ive allways worked on the idea of a pir/eicr is to evaluate the installation against the CURRENT version of the regs, if the install was to an earlier version of the regs then issues such as above would be a code 4 but now what would they be a C3 or no code??
 
Last edited by a moderator:
I have no idea what they didn't like about your coding, maybe they had cause and maybe not!! But they can't and/or shouldn't be telling you how THEY want it done!! You follow the national guidelines laid out in the relevant authorities, which i guess would be the IET in this case...
 
Just to put a spanner in the works.
Whilst the IET along with the BSI, has the responsibillity for conceiving, formulating, writing and publishing the Regulations.
In actual fact, the NICEIC, along with representatives of just about every other electrical organisation provide members of the comitee that does the work.
So technically the NICEIC do write the Regulations, or make the rules.
 

Reply to Code 2 for non RCD lights in a bathroom in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
309
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
832
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
930

Similar threads

SOLVED Thanks for all the help. It was nothing to do with the smoke detector. In this new hole (where there will be a light fitting) three white...
    • Like
2
Replies
24
Views
3K
Thank you. We do have a window. Do you think my idea (even if is adds complexity) is workable? Nothing fundamentally wrong that I am missing?
Replies
6
Views
729

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top