Afternoon all,

just completed a domestic PIR and could do with some guidance on the coding of this situation;

Installation converted from TT to PME approx 12 years ago and the property was rewired around the same time and a spilt load board installed. However the 100mA RCD covering the TT system was left inplace between meter and CCU which effectively covers the non RCD protected side of the board (circuits to Lights and Immersion).

Code 2 because it's not 30mA?

Any help appreciated.

Thanks

Will.
 
Code 4, does not comply with current edition of BS 7671.

Up until the 17th there never was a requirement to provide additional protection to buried cables etc.
 
Afternoon all,

just completed a domestic PIR and could do with some guidance on the coding of this situation;

Installation converted from TT to PME approx 12 years ago and the property was rewired around the same time and a spilt load board installed. However the 100mA RCD covering the TT system was left inplace between meter and CCU which effectively covers the non RCD protected side of the board (circuits to Lights and Immersion).

Code 2 because it's not 30mA?

Any help appreciated.

Thanks

Will.

Just a note. Did you make sure that the 100mA Rcd was in fact a RCD and not a ELCB. Did you test it's operation.
 

Reply to Code 2 or code 4 ? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
814

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
  • Question
Good point, I was assuming an up-front RCD is for fault protection within DB, etc, and to cover for a failed RCBO for fault conditions, not as...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top