I'm getting in a bit of a muddle as to whether this is a code C3 or no code.

This is an EICR. The CU has a 100mA main switch. The lights have 100mA protection the rest of the install has 30mA protection. It is a TT.

The Best practice guide clearly says no RCD protection in this scenario is a C3, but it doesn't state if this has to be 30mA.

Cheers all.

Ps.. also reg 701.411.3.3 clearly says 30mA needed.
 
Last edited:
411.5.2 says a RCD doesnt need to be fitted, but is preferred.
701.411.3.3 is for rooms containing a bath or shower, so you have one or more of those in the property?

Edit are any cables buried in walls?
 
Plenty of cables buried in walls.

Yes, it does it serve a bathroom and there is supplementary bonding in place.
 

Reply to Code for no 30mA protection on lights? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I would C2 this, cable is not suitable for the environment its installed in, we would C2 a socket for equipment likely to be used outside , cable...
Replies
11
Views
971
As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top