Sigh..
Okay.
The Management of Health and Safety at Work Regulations 1999 - just in case you are not sure, this a legal thingy
3.—(1) Every employer shall make a suitable and sufficient assessment of—
(a)the risks to the health and safety of his employees to which they are exposed whilst they are at work; and
(b)the risks to the health and safety of persons not in his employment arising out of or in connection with the conduct by him of his undertaking,
(6) Where the employer employs five or more employees, he shall record—
(a)the significant findings of the assessment; and
(b)any group of his employees identified by it as being especially at risk.
You are probably not at work in a dwelling and so the requirements of the Management of Health and Safety at Work Regulations won't apply.
But as I said, I wouldn't put a dwelling into a stereotype. I would assess it properly and dynamically.
BS 7671:2008 2011
411.3.3 Additional Protection
In a.c. systems, additional protection by means of an RCD in accordance with Regulation 415.1 shall be provided for:
(a) socket-outlets for use under the supervision of skilled or instructed persons, or
(b) a specific labelled or otherwise suitably identified socket-outlet provided for connection of a particular item of equipment.
BS 7671:2008 2015
411.3.3 Additional Protection
In a.c. systems, additional protection by means of an RCD in accordance with Regulation 415.1 shall be provided for:
(a) where, other than for an installation in a dwelling, a documented risk assessment determines that the RCD protection is not necessary, or
(b) a specific labelled or otherwise suitably identified socket-outlet provided for connection of a particular item of equipment.
So what is the big difference.. well with the 2011 edition of BS 7671 and prior, it was considered acceptable for a place of work to negate the need for RCD protection as a skilled or instructed person would attend in the role of caretaker or maintenance guy. Basically someone who had sufficient knowledge to avoid danger.
With the changes to definitions in 2015, this skilled persons would now need 'adequate education' to satisfy this role.
In most cases the person in schools and similar roles would not necessarily possess the adequate education to remain in the role so the regulation was reworded to say a risk assessment is need.
Nobody wants to publicly announce what the 'adequate education' of a caretaker, landlord or similar should be...
Translated that means 'we know your guy may not have adequate education, or his education may be questionable. So carry out a documented risk assessment instead'.
So while an older standard could rest on the observation by skilled/instructed persons, it now needs a documented risk assessment.
I am not saying the installation is less safe, the regulations have tightened definitions that were more loosely interpreted and has applied tighter control procedures that clearly some people have never seen or asked for.
Okay.
Perhaps I have repeated myself, only because you haven't answered.
You stated that you asked for a task specific Risk Assessment.
Such a statement suggests you expect there to be a written Risk Assessment.
There's no law requiring written Risk Assessments.
Yes documenting Risk Assessments can be useful, but still there is no Statutory requirement to do so.
The Management of Health and Safety at Work Regulations 1999 - just in case you are not sure, this a legal thingy
3.—(1) Every employer shall make a suitable and sufficient assessment of—
(a)the risks to the health and safety of his employees to which they are exposed whilst they are at work; and
(b)the risks to the health and safety of persons not in his employment arising out of or in connection with the conduct by him of his undertaking,
(6) Where the employer employs five or more employees, he shall record—
(a)the significant findings of the assessment; and
(b)any group of his employees identified by it as being especially at risk.
So when you asked for the Risk Assessment, did they respond that they had not conducted one, or just that they didn't have a written copy?
Still no explaination as to why you treat dwellings differently to Schools. Perhaps electricity in dwellings is different from that in Schools?
You are probably not at work in a dwelling and so the requirements of the Management of Health and Safety at Work Regulations won't apply.
But as I said, I wouldn't put a dwelling into a stereotype. I would assess it properly and dynamically.
You mentioned reference guides, summary sheets and NICEIC pocket guides. What you need is none of those, you just need a copy of BS7671.
As long as you conduct your inspection in accordance with BS7671, everything will be fine.
Problem with your coding, is it is not in accordance with BS7671.
You are basically stating that something is unsafe today which the Regulations said was safe last year.
There is no way that any edition or amendment of BS7671 is ever going to say earlier editions or amendments had unsafe requirements.
BS 7671:2008 2011
411.3.3 Additional Protection
In a.c. systems, additional protection by means of an RCD in accordance with Regulation 415.1 shall be provided for:
- socket-outlets with a rated current not exceeding 20 A that are for use by ordinary persons and are intended for general use, and
- mobile equipment with a current rating not exceeding 32 A for use outdoors.
(a) socket-outlets for use under the supervision of skilled or instructed persons, or
(b) a specific labelled or otherwise suitably identified socket-outlet provided for connection of a particular item of equipment.
BS 7671:2008 2015
411.3.3 Additional Protection
In a.c. systems, additional protection by means of an RCD in accordance with Regulation 415.1 shall be provided for:
- socket-outlets with a rated current not exceeding 20 A, and
- mobile equipment with a current rating not exceeding 32 A for use outdoors.
(a) where, other than for an installation in a dwelling, a documented risk assessment determines that the RCD protection is not necessary, or
(b) a specific labelled or otherwise suitably identified socket-outlet provided for connection of a particular item of equipment.
So what is the big difference.. well with the 2011 edition of BS 7671 and prior, it was considered acceptable for a place of work to negate the need for RCD protection as a skilled or instructed person would attend in the role of caretaker or maintenance guy. Basically someone who had sufficient knowledge to avoid danger.
With the changes to definitions in 2015, this skilled persons would now need 'adequate education' to satisfy this role.
In most cases the person in schools and similar roles would not necessarily possess the adequate education to remain in the role so the regulation was reworded to say a risk assessment is need.
Nobody wants to publicly announce what the 'adequate education' of a caretaker, landlord or similar should be...
Translated that means 'we know your guy may not have adequate education, or his education may be questionable. So carry out a documented risk assessment instead'.
So while an older standard could rest on the observation by skilled/instructed persons, it now needs a documented risk assessment.
I am not saying the installation is less safe, the regulations have tightened definitions that were more loosely interpreted and has applied tighter control procedures that clearly some people have never seen or asked for.