Code query | on ElectriciansForums

Discuss Code query in the UK Electrical Forum area at ElectriciansForums.net

bigspark17

-
Arms
Joined
Sep 22, 2012
Messages
1,560
Reaction score
733
Location
wales
Metal clad sw fuse 80A.. Live and neutral outgoing leave throught same knockout hole but L and N supply from dno cutout enter through diferent holes.! Be intrested to see peoples thoughts on coding with regards to protection aggainst electromagnetic effects where cables enter.. I coded it c2.! And yes all knockouts were grommeted
 
Definitely c2 as its potentially dangerous, it can't be a c1 as its not immediately danger and I can't be a c3 as that's never been acceptable.

i know that isn't the exact meaning of the coding but a good rule of thumb
 
On a risk assessment basis the probability of the fault occurring is very low but the potential to cause harm / damage if a fault occurs is very high so I would tend toward C2 as well. Mainly because there is a specific regulation prohibiting this action.
 
With regard to domestic the demand on the supply is normally too low for the issues of eddie currents to have a runaway effect .. you would be looking at demand in excess of 200amps for a dangerous situation, there was a recent thread on this and the main contribution to this effect creating a problem is when there is a metal sheath or armour grounding to the metal box ...MICC, SWA, Conduit etc this magnifies the effect and this is where even lower range currents can generate excessive heat due to eddie currents .... I have never seen any issue with <200amp where the cables don't have an earthed sheath or mechanical protection that is grounded 'at the switchfuse in this example'.

I thus don't rate it as a C2 but from a regulation point of view that just have it as a blanket issue then yes it can be seen as a code 2.
 

Reply to Code query in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
395
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
986
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top