What would you code recess lights in bathroom,no Rcd ,no supplementary bonding.
Also correct IP rated lights l one over bath area Zone 1...230v... woulld you be ok with that, it’s below the height require2.25m I think, you could touch it with out stretch arms.
 
Its an interesting one. The BPG #4 has an example on page 7 of a recessed lamp above a bath saying:

"Recessed luminaire above a bath (outside the zones) that is not IPX4 would not warrant a comment"

However, to me that just seems wrong.

That example is almost exactly what I had in my own flat and for years did not bother me as I don't make it a habit to change lightbulbs naked and wet, but for guests I did get a bit more concerned and eventually they got a IP6? light fitted instead. So I would go with the above, if its no RCD and hand-reachable from the bath I would say C2.
 
The 2.25m measurement is from the floor around the bath, not the bottom of the bath itself, which may be up to about 300mm above the floor, putting the light fitting in easy reach.
This is one example of where the upgraded reg. took a backwards step. The original wording was "out of reach of a person using a shower or bath" and would have covered this scenario.
 
The 2.25m measurement is from the floor around the bath, not the bottom of the bath itself, which may be up to about 300mm above the floor, putting the light fitting in easy reach.
This is one example of where the upgraded reg. took a backwards step. The original wording was "out of reach of a person using a shower or bath" and would have covered this scenario.
You'd hope commonsense would prevail here? If the water jets from the shower can reach the fitting, irrespective of light mounting height, then the appropriate level of IP rating should be given,, and this reasoning given to the customer. If they don't agree then it's on them, not you
 
What would you code recess lights in bathroom,no Rcd ,no supplementary bonding.
Also correct IP rated lights l one over bath area Zone 1...230v... woulld you be ok with that, it’s below the height require2.25m I think, you could touch it with out stretch arms.

Bathroom lights are often one of the potential fail issues on the recent EICRs I've done since until even very recently there was no requirement for RCD on lighting and the install of supplementary bonding was patchy at best. I'd say that most new builds up to 2015 I've seen have it only partly - even if it was a requirement.

One other thing that has to be considered though - plenty of the recessed downlights I've seen installed are actually Class 2 - so they don't technically need supplementary bonding even when not protected by an RCD. The same can be argued for 12V fittings, (When installed properly so that 230V cannot touch any metal parts).

On the other hand, I've never seen a properly installed downlight in more recently built properties, as the basic insulation is always well outside the fitting - that could be either a C2 or C3 depending on judgement and how 'accessible' it is.

So the chain I follow is:

1. Is RCD installed
2. If not, are they Class 2 fittings
3. If no, is supplementary bonding present (At this point I usually test between relevant parts with a wander lead to check for effective bonding or not)
4. If no to all the above, then C2

With zones, a lot of firms just seem to C2 anything but obvious 'bathroom lights' in a bathroom, but if they are outside the zones then they do not need to be IP rated so arguably cannot get a C2 for that - though they could be raised as an issue under general 'suitability of accessories for external influences'.

To be honest, I've never actually seen a fitting so badly damaged by steam in a bathroom that it becomes unsafe.
 
Bathroom lights are often one of the potential fail issues on the recent EICRs I've done since until even very recently there was no requirement for RCD on lighting and the install of supplementary bonding was patchy at best. I'd say that most new builds up to 2015 I've seen have it only partly - even if it was a requirement.

One other thing that has to be considered though - plenty of the recessed downlights I've seen installed are actually Class 2 - so they don't technically need supplementary bonding even when not protected by an RCD. The same can be argued for 12V fittings, (When installed properly so that 230V cannot touch any metal parts).

On the other hand, I've never seen a properly installed downlight in more recently built properties, as the basic insulation is always well outside the fitting - that could be either a C2 or C3 depending on judgement and how 'accessible' it is.

So the chain I follow is:

1. Is RCD installed
2. If not, are they Class 2 fittings
3. If no, is supplementary bonding present (At this point I usually test between relevant parts with a wander lead to check for effective bonding or not)
4. If no to all the above, then C2

With zones, a lot of firms just seem to C2 anything but obvious 'bathroom lights' in a bathroom, but if they are outside the zones then they do not need to be IP rated so arguably cannot get a C2 for that - though they could be raised as an issue under general 'suitability of accessories for external influences'.

To be honest, I've never actually seen a fitting so badly damaged by steam in a bathroom that it becomes unsafe.
Agree-these are class1 fitting, I can remember when fitting fans in bathrooms they had to be low voltage if anywhere near the bath area.
The Code for the lights I would give C2 mainly for no Rcd protection.
 
To be honest, I've never actually seen a fitting so badly damaged by steam in a bathroom that it becomes unsafe.
To be honest you don't find that many bathrooms with steam rooms in them and even then the "steam" isn't at full temperature as above 59°C your skin will start to blister.
I assume by steam you mean the water vapour that subsequently forms condensation damaging the fittings in which case I have seen some quite badly corroded fittings over the years
 

Reply to Codes for Eicr...just wondering in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
ok cheers for the help lads
Replies
7
Views
711

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top