Hello all..

I have just completed an EICR.

The earths for the ceiling lights are wrapped around each other (neatly and well, numerous times) and sheathed in old green sheath. They are then poked up into the ceiling void. This is obviously all wrong nowadays, but I can't decide if it's a C2 or C3. I would think C3? They are making a very good connection with each other, probably better than sheathed separately and clamped down with a screw too tightly! However, It would be good to hear opinions :)
 
Last edited:
Probably as good as the twist on wire connector nuts, which I'm surprised are still permitted, and as it tests satisfactorily and unlikely to be disturbed in normal use I would think C3 too.
 
Code 2 it is not a mechanical connection nor are they suitably enclosed.
Could I ask if you ever did this in the past Westward? Genuine question as I believe you were around back in the olden days ;-) (could get a temporary ban for that). But it really is a genuine question. Was it common place, even amongst good electricians to terminate the earths this way?
 
Could I ask if you ever did this in the past Westward? Genuine question as I believe you were around back in the olden days ;-) (could get a temporary ban for that). But it really is a genuine question. Was it common place, even amongst good electricians to terminate the earths this way?
Never done it (I'm not that old) and I doubt it was ever a prescribed method for terminating cpcs.
 
526.1 Every connection between conductors or between a conductor and other equipment shall provide
durable electrical continuity and adequate mechanical strength and protection.
 
not suitably enclosed though.... however good the joint is... it cant just be poked into the ceiling
526.1 Every connection between conductors or between a conductor and other equipment shall provide
durable electrical continuity and adequate mechanical strength and protection.
I think we are all in agreement it is a non-compliance. The issue is, is it a C2 - Potentially Dangerous or C3 in need of an improvement?
EICR's can be very subjective and we all have our reasons and opinions, that's the beauty of forums like this. Everyone can state theirs rightly or wrongly. We are never going to always agree!
 
I think we are all in agreement it is a non-compliance. The issue is, is it a C2 - Potentially Dangerous or C3 in need of an improvement?
EICR's can be very subjective and we all have our reasons and opinions, that's the beauty of forums like this. Everyone can state theirs rightly or wrongly. We are never going to always agree!
No enclosure, not terminated properly. Its a c2
 

Reply to Coding for earths wrapped around each other? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
554
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
992
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
924

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top