I’ve had a disagreement with a colleague on this. Installation has 100ma rcd main switch.
Some circuits (5) on this side and further 4 on the
30ma rcd side.

what is the coding for this?
 
C3, as in that the circuits not protected by 30mA RCD could be improved to increase safety. wouldonly be C1 or C2 if immediate or potential danger present (respectively).
 
It depends on what the circuits which don't have 30mA protection are, you need to supply more information.

Without further information I would say no code unless something you haven't told us would mean these circuits require 30mA protection. If you at least specified the basic type of installation such as domestic or non-domestic it would help massively.
[automerge]1597180001[/automerge]
C3, as in that the circuits not protected by 30mA RCD could be improved to increase safety. wouldonly be C1 or C2 if immediate or potential danger present (respectively).

Why a C3? They haven't yet told us anything that suggest these circyits require 30mA protection.
 
It depends on what the circuits which don't have 30mA protection are, you need to supply more information.

Without further information I would say no code unless something you haven't told us would mean these circuits require 30mA protection. If you at least specified the basic type of installation such as domestic or non-domestic it would help massively.
[automerge]1597180001[/automerge]


Why a C3? They haven't yet told us anything that suggest these circyits require 30mA protection.
i assume (perhaps wrongly) that OP is referring to a domestic install, probably to 16th Ed., in which case 30mA RCD protection to cables in walls blah, blah and lighting circuits, maybe unprotected circiuts in a bathroom, would be improved by fitting 30mA RCD protection, so a C3 for improvement recommended.
 
Thanks I’ve always put as c3 but colleague said C2 as it’s a TT System. Could not see that anywhere

You still haven't explained why it needs 30mA protection at all?

Is it domestic? Are they socket circuits? Are there cables buried <50mm? Are they lighting circuits?
 
Guessing at domestic install? Also going to assume that TT the Zs max have been exceeded. (C3 411.3.2.2)
However a 100ma RCD is provided for fault protection and A 30ma RCD for fault/additional protection.
I would code it as C3 if it is what I’m thinking of, a domestic install to the 16th edition. Most likely because of a lighting circuit not having additional protection at 30mA (411.3.4)
In my opinion, it’s only a C2 if no RCD is provided for fault protection on a TT system (411.5.2).
 
Probably depend when it was built and if there's no RCD then it usually required equipotential bonding, earthed conduit for wires in walls under 50mm and all that.
I don't think it would meet current Regs would it all circuits require RCD protection and 100ma is more protection of fire?(is that right) not electric shock.
 

Reply to Coding for lack of 30ma rcd protection - TT system in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
298
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
I would probably C3 it, based on no contact with sharp edges, all the terminations being tight, and no signs of any thermal damage. With all...
Replies
2
Views
960

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top