[ElectriciansForums.net] Coding question - Twin and Earth Tails
As above really. First time I have seen this but its basically 16mm twin and earth connected straight into the outgoing side of the meter, and into the consumer unit. Quality. Couldn't quite get a picture of the external MET but can confirm an additional cable has been added to bring the size of the main earth up. So two main earths if you like. The 'additional earth' is sleeved as well (not insulated at-all).
TNS, cut out fuse size not known (says 100Amp on sticker but unlikely round here). Low demand anyway and certainly no thermal damage.
I'm thinking code 2 but interested in others thoughts on this one?
 
If there's no sign of thermal damage and it's a firm connection with not much chance of over load then I'd C3 personally - Only thing that could happen to make it dangerous would be an lengthy overload but it would take a lot to melt 16mm I'd think, especially in Free Air.

Edit - forgot the basic insulation issue, so that would push it to C2. Good luck getting the energy supplier to come out to change it though if it's not one of the big ones.

Surprised any meter installer connected it directly, but that looks like their covers at the meter connectors.
 
Last edited:
If there's no sign of thermal damage and it's a firm connection with not much chance of over load then I'd C3 personally - Only thing that could happen to make it dangerous would be an lengthy overload but it would take a lot to melt 16mm I'd think, especially in Free Air.

Surprised any meter installer connected it directly, but that looks like their covers at the meter connectors.

Thanks for that - I think it has been installed by a meter installer. The 16mm is tinned copper as well, so it's been there a while. - a lot longer than the consumer unit
 
Nothing wrong with the cable as such, but only basic insulation at the meter, so it should be coded C2 just the same as if it was double insulated singles with the basic insulation exposed.
 
Hiya Marcus. Brown and blue labelled to make sure, eh?
C2 ...exposed, single insulation at meter entry. Besides being crap.
 
If it’s accessible then it’s a C2, basic insulation exposed outside of a suitable enclosure, basic insulation cannot be used on its own as a form of protection.
Good point - I was thinking of the rating but forgot about basic insulation. Though I've often seen tails with the outer sheath trimmed back, especially in Henley Blocks.
 
Code 2 is then. I think I softened on it when I realised it was never going to overload but yes there is only basic insulation at the connection to the meter. One for the experience bank that. Thank you.
 
This is one of those tricky ones if it's rented. Only way to carry out the required remedial work would need the energy company to send out a meter guy, and some of the companies seem very loathe to do that in my recent experience and might well not do so within 28 days.

So there is no practical way for the landlord to comply with the current law as it's written.

Question: Would self amalgamating tape of the right kind wrapped round count as additional protection for this purpose?
 
This is one of those tricky ones if it's rented. Only way to carry out the required remedial work would need the energy company to send out a meter guy, and some of the companies seem very loathe to do that in my recent experience and might well not do so within 28 days.

So there is no practical way for the landlord to comply with the current law as it's written.

Its actually a house move with buyer requesting an EICR. Seller still there. But you are right about it being a pita. As soon as I spotted it I informed the current owner what to (try) to do about it and then she spent the afternoon on the phone trying to sort it. Not good. Apparently the energy supplier will only fix it if they, at the same time, upgrade to a smart meter. So that's what's going to happen (and hopefully an isolator as well).
 

Reply to Coding question - Twin and Earth Tails in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top