Hi all,

i I have my first combi to wore up next week. I have got the drawing here for the controller and it gives me terminals for a hot water cylinde stat,The system has no cylinder in it s it's a combi so I assume that somewhere in the boiler it has a built in stat? Like I said this is my first boiler job so I am a bit unsure with regards to the stat. I am confident with the wiring of the valves and room stats etc. Any advise would be appreciated.

thanks
 
Last edited:
Re: Combo boiler cylinder stat

If you know what type of boiler it is, download the installation manual for it as that will tell you what you need to know.

A combi only requires a one channel programmer and room stat for the heating. The hot water doesn't need any external control as it just functions when a hot tap is opened using sensors inside the boiler.
 
Thanks, to provide a bit more information, it's a second hand oil combi boiler I'm told as if not yet been to the job. The heating has been split into two zones with 2-port valves. I will be putting two stats upstairs and then one downstairs to control the valves. I will wire it in s-plan plus. It's the hot water I'm not sure about as its my first boiler job. Any help or tips would be great
 
If it's oil combi? Then don't worry about the hot water the boiler will take care of that once anyone turns on a tap the boiler will fire up.

if you get to site and see a tank then just wire the two port up to timer via the cylinder tank stat

if you understand how to wire s-plans etc then I don't think you have anything to worry about.

combi boilers make wiring easier.
 
Last edited:

Reply to Combi boiler cylinder stat in the Central Heating Systems area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
401
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
987
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I have just looked at the wiring diagram on line and there are a lot of internal links which if in the wrong terminal could put 230 volt onto...
Replies
10
Views
828
T
  • Article
Indirect (Boiler Fed) Megaflo Doesn't Stop Heating Hi, I noticed yesterday that when my HW is on, that the boiler runs constantly... I even...
Replies
0
Views
241
techweb
T

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top