Just make sure you fuse the combi-boiler SFCU at 3A and do the same for the softener.
Oh, and use heatproof flex on any cabling which runs inside the boiler itself...
Thanks, im only doing the supply, the boiler wiring will be down the heating engineer
Thanks, im only doing the supply, the boiler wiring will be down the heating engineer
Just a quick question; is there an option of running boiler off an rcbo as this should be the preferred method, a fault on any other circuit married up to same rcd could see a loss of hot water and heating as well, if the property has other means of heating (gas fires) then not such a big problem.... loss of heating when its minus 10 outside because of an unrelated fault is a thought to be considered in design, thus should be avoided.
have you tried using one of these?This was also my preferred choice but was unable to physically fit an rcbo into the CU
Just a quick question; is there an option of running boiler off an rcbo as this should be the preferred method, a fault on any other circuit married up to same rcd could see a loss of hot water and heating as well, if the property has other means of heating (gas fires) then not such a big problem.... loss of heating when its minus 10 outside because of an unrelated fault is a thought to be considered in design, thus should be avoided.