I suppose the grey and brown of each valve could be connected together if you can't connect the greys to the heating unswitched supply.

Nope, that would tie the two stats together when both valves are open, backfeeding via the boiler SL and preventing one valve closing while the other stat is still calling for heat. Greys must be fed with permanent live.
 
Nope, that would tie the two stats together when both valves are open, backfeeding via the boiler SL and preventing one valve closing while the other stat is still calling for heat. Greys must be fed with permanent live.

My thinking was connect the brown of zone 1 (say) heating valve to the grey of zone 1 heating valve and the brown of zone 2 heating valve to the grey of zone 2 heating valve. Can't see how this would backfeed. In this case the greys are only live when the stats are calling as opposed to being permanently live.
 
In this case the greys are only live when the stats are calling as opposed to being permanently live.

Not true, greys can be made live from SL backwards through valve microswitch. See pic, shown with both valves open. When stat 2 or its programmer contact removes the supply from valve 2's motor, the motor would remain energised via the path shown dotted until stat 1 is also satisfied. Then both valves would close at once. And vice versa of course.
[ElectriciansForums.net] Combi boiler wiring advice please
 

Reply to Combi boiler wiring advice please in the Central Heating Systems area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
430
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I have just looked at the wiring diagram on line and there are a lot of internal links which if in the wrong terminal could put 230 volt onto...
Replies
10
Views
831

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top