I have a problem and I think I have a solution but wanted to throw it out there to check it is acceptable..
First floor flat with two fuseboards - 1 24hr and 1 Night time economy. The boards are being supplied by two armoured cables coming from separate isolators/meters (60A) from the ground floor.
No clear identification on the armoured cable but possibly 16mm2.
Looking to have the two existing meters replaced with one and the suppy fuse etc upgraded to 100A.
Instead of running a fresh armoured cable from the ground floor, I was considering whether the two existing cables could be combined and therefore have capacity for the increased load?
Taking 25mm2 tails out of the new meter into Henley Blocks and have the Live & Neutral from each existing armoured cable combined and the arrangement reversed at the fuseboard.
I hope I've explained myself clearly there.
Ran this past Niceic technical support and they suggested it was feasible..
First floor flat with two fuseboards - 1 24hr and 1 Night time economy. The boards are being supplied by two armoured cables coming from separate isolators/meters (60A) from the ground floor.
No clear identification on the armoured cable but possibly 16mm2.
Looking to have the two existing meters replaced with one and the suppy fuse etc upgraded to 100A.
Instead of running a fresh armoured cable from the ground floor, I was considering whether the two existing cables could be combined and therefore have capacity for the increased load?
Taking 25mm2 tails out of the new meter into Henley Blocks and have the Live & Neutral from each existing armoured cable combined and the arrangement reversed at the fuseboard.
I hope I've explained myself clearly there.
Ran this past Niceic technical support and they suggested it was feasible..