B

brennybig

Hi all. I am replacing three CU's all with 16mm meter tails with one CU 100Amp ( conversion of three flats back into a single dwelling). Very difficult to install new 25mm tails as wiring under a tiled floor and new CU is 10 metres from the meter. Is it acceptable and are there any problems as a result of combining all three 16mm tails using henley blocks and running 25mm from the block to the new CU? I should add that all three 16mm tails have a fused 60 amp isolator near the meter.

Cheers

Brenny
 
hi brennybig
the first thing to do is check the overall load expected of the new c/u final circuits.
A pair of16mm tails can take 87 Amps when clipped direct at 30 degrees ambient temp.according to my calcs! so as long as your calcs using diversity for the new circuits comes to less than 87 Amps i would personally use one pair of the 16mm tails and make safe the other pairs by disconnection or placing in their own henly blocks. the reason i would do this is because if all three are connected and some muppet removes only one main 60 amp fuse and not all three (from what you have written it reads as three seperate main fuses) then confusion rains along with charcoaled bits of muppet. One fuse, one pair of supply cables to one consumer unit.
Thats my opinion anyway.
 
Thanks miner69er. The necessity of turning off three isolating fuses to isolate the new CU is one of my main concerns. I have considered using henley blocks on the supply side also and fitting a single switched 100 amp isolator there to overcome this problem. The dwelling has three floors, hence three ring mains plus another for the kitchen so a single 16mm tail is not an option. I am really trying to avoid the customer the expense of having to install new 25mm tails, 10 metres long in a safe zone with earthed sheating. Unless anyone knows of a 30mA time delayed RCD 100A isolator switch that I could protect the tails with?

Cheers

Brenny
 
SWA all the way I'm afraid, the time and hassel making the old stuff work will outweigh the additional cost, and you wouldn't need to put the submain on an RCD. Personal opinion
 
The floorspace above has the tiled floor and is joisted at 90 degrees to the direction I want to go, hence any option that can utilise the existing cables is preferable.

Brenny
 
Have thought about using SWA but I still have to bury it in the wall for asthetic reasons and given how difficult it is to work with I would probably go with the earthed sheating option instead. I should add that with the exception of the supply wall, all walls involved are internal on both sides. Thanks for all your help.

Brenny
 
Please don't take this the wrong way but are all the meter tails from the same origin ie are they all from the same single phase cut out and not a three phase supply split just checking as combining them would be lethal If it was the latter
 
All three isolators are fed from the same pair of henley blocks which are connected to a single phase. Oddly enough the cutout fuse holder is of the three phase variety but only one phase is being used. Perhaps in the past a phase was used for each flat each with a separate meter but that is only a guess.

Cheers

Brenny
 
Onstream fitted a new smart meter at the house and fitted an isolator for free when I requested it. The new cutout fuse is 80 amps ( the fitter told me that this is the biggest they will supply now and I would have to contact the DNO to request a bigger one and explain why it is required) and they have used 16mm meter tails. Why then am I having to struggle to fit 25mm tails to the CU?

Cheers

Brenny
 

Reply to Combining meter tails in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
591
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
949

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
936
  • Question
Normally you'd install either a fuse-switch or a switchfuse at the incoming supply position rather than a DB, this gives you some hope of...
Replies
10
Views
2K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top