a client needs a 32a single phase commando installed so they can charge the forklift via a 7.2kw charger.

There is currently a redundant ring circuit adjacent, tested ring continuity and a is ok on the 32a RCBO.

Apart from sounding a bit piky can anyone see anything unsafe with the temporary arrangement?
 
a client needs a 32a single phase commando installed so they can charge the forklift via a 7.2kw charger.

There is currently a redundant ring circuit adjacent, tested ring continuity and a is ok on the 32a RCBO.

Apart from sounding a bit piky can anyone see anything unsafe with the temporary arrangement?
 
You will have a fully loaded circuit for the charger on its own and presumably long periods, the legs of this redundant ring,they may have difference in the shared load
Maybe split the ring at that point and check the difference in the resistance of each leg,see if its going to stress any one side,
then consider blanking off any other outlets
 
That is Mable.
you remembered her name! That means a lot that does westie.
Has she settled in now.
No man. It's a long and very sad story, but I had to let her go to another owner, due to family pressures and my own impetuous actions when I got her as too-soon replacement for my previous dog. Shes doing just fine though, and probably forgot about me now. Thanks for asking anyway matey.
 

Reply to Commando socket question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Better/Smart/intelligent/expensive generators require two earth spikes set ~10-15m apart. They check the resistance between spikes and will...
Replies
5
Views
902
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
777
  • Question
:) The reason is cost, it only needs to allow fault disconnection and possibly extraneous bonding if TN-C-S (another thread...) 4C cable is...
    • Like
Replies
11
Views
2K
  • Question
Single Pole, Single Pole Switched Neutral, and Double Pole are all different things. Hager RCBO's are Single Pole. I was recommending Single Pole...
Replies
33
Views
5K
  • Locked
  • Solved
Therein lies the problem. I see no merit in further circular debate, so will bow out of this discussion.
    • Like
2 3
Replies
55
Views
7K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top