Back in this fab shop today replacing 400v 4 pin commando sockets got me thinking there 3 phase and earth so I gather the welding sets are balanced loads but has anyone installed or come across the 5 pin ones were you require a neutral
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Commando sockets for welding sets in the UK Electrical Forum area at ElectriciansForums.net
Calling Planet Earth.
Get real!
Ok thanks for all your input the ones I've been replacing today the armours are already in but there all 4 core ie 3 phase and earth so must limit them to certain welding sets that answers my question not all welding sets are balanced loads some need a 5 core cable for the neutral cheers guys
Tony , have you been at that bloody puzzle and forgot your pills again ? :ihih: ( No offence meant , of course.)
Farmelectrics , i think Tony means you can always use the swa as a earth so you could in fact install 5 pin on a 4 core .
Edit ; But personally i do prefer to run 5 core , i know there is no real need but i just like the reassurance that a good earth is not only resting on a gland that may not have been made off 100% correctly .
And before it is mentioned that the gland should be correctly made off " End of story" , if i made every one off on our firm then i would except that but i don't !
and some weldsets only use 2 phases
most of the small spot welding trigger tong guns just use 2 phases....