A top quality EICR report attached.
I'm detecting an increase in opportunists looking to scare the bejesus out of landlords in particular. This report is utter crap. Everything ticked or N/A on the inspection schedules to suggest all is satisfactory but then some belter C1's in observations, including 'Full Rewire Required". Same chap uses scaremongering of the likes of 'hefty fines or even imprisonment' for negligent landlords, and was offering EICR's for as little as ÂŁ75 including VAT at one point.
I'm to visit the site this morning to try and get a sense of it. The same chap has already upgraded the consumer unit but does it need a rewire? I mean 'Resistance values low for all circuits?' - I take it he means IR but schedule of test results indicate all OK. What will I find.
I feel something should happen to stop this sort of carry on - but what?
A top quality EICR report attached.
I'm detecting an increase in opportunists looking to scare the bejesus out of landlords in particular. This report is utter crap. Everything ticked or N/A on the inspection schedules to suggest all is satisfactory but then some belter C1's in observations, including 'Full Rewire Required". Same chap uses scaremongering of the likes of 'hefty fines or even imprisonment' for negligent landlords, and was offering EICR's for as little as ÂŁ75 including VAT at one point.