An MCB rated as stated at 10Ka are generally used more in a commercial situation and if you ask at a wholesalers for an MCB for domestic purposes you will normally be offered a 6Ka rated MCB.
Miniature Circuit Breakers (MCB) guide | Newey & Eyre - http://www.neweyandeyre.co.uk/guide-to/miniature-circuit-breakers
say;
i.e. An MCB’s circuit rating is given in Kiloamps (KA), and this indicates the level of its ability to work. For example a domestic MCB would normally have a 6KA fault level, whereas one used in an industrial application may need a unit with a 10KA fault capability.
I would never ask a wholesaler what protective device I should use for a particular application.
 
What exactly is a commercial mcb?

There are two standards for MCBs, 60898 covers MCBs for domestic and similar applications and 60947 covers other applications.
Generally a 60898 mcb will have a 6kA rating and won’t necessarily comply with 60947, whereas a 60847 mcb will generally have a 10kA+ rating and will be ‘dual rated’ to 60898 also
 
It's not a trick question some manufacturers produce an RCBO in B & C curve 6 and 10 KA domestic short neutral fly leads and long for three phase.
 

Reply to the thread, titled "Commercial CU change - legalities etc." which is posted in Commercial Electrical Advice on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top