Hi All,

Being doing a commercial EICR over night (7-7) for the past week, still got a good few nights to go.

The installation is most likely 40-50 years old, was originally done well. About 5 years ago they had another contractor redo a lot of the electrics to accommodate the current owner. The previous electricains work is unreal, he has completely ruined the installation.

I'm not 100% sure how to approach this. There's a lot a minor things which need doing which I will report back, but the lighting in some of the areas is unreal. The previous contractor had used SY cable everywhere, not correctly terminated at any point, which I found out is carrying a healthy 157v on the braiding. Basically every earth has been cut out throughout the lighting, mainly class 2 fittings, but due to the fact a lot of he circuits are new and all the existing work has an earth, would that be a C2. As it should comply with when he installed it.

Also getting 287v back down a neutral when not connected via a circuit fed by a Seperate DB on the other side. Earths used as feeds in some cases, some lighting circuits supplied via 2/3 circuits, all with no CPC and low IR. Due to the fact it's suspended ceilings everywhere etc... I was thinking it might just be easy to just redo a lot of the lighting instead of trying to break it down and see what's salvageable.

What would any of you do?
 
You are doing the report at the moment so continue with that until complete but it maybe prudent to advise your client of the nature of the findings so far to prewarn them, but only provide full detail in the report or you may miss things and may be asked to stop the report.
The lighting is bad and the crossover of circuits is very worrying.
You state mainly class II fittings which means some are not class II so lack of earthing would be a C2 classification.
It may be easiest to keep light fittings and replace wiring runs but the layout of the circuits will determine the most appropriate method of rectification.
 
It’s a shame when an old but perfectly useable installation is butchered by some body who doesn’t know and/or care what they are doing.
I’ve come across it all too often.....although nothing as bad as you describe.
Basically condemn it with C2 and FI comments where needed and as others have mentioned, worry about sorting it out later on when the report is completed.
 
I am puzzled. 157v on braiding? Is that not a real and immediate risk of electric shock? If so would it not warrant a C1. In which case the person ordering the work should be informed in writing and the inspection halted until that situation has been dealt with???
Sounds a bit dramatic:screamcat:
 
Always good to know how others carry out their work, when doing an EICR would you simply test the IR on a DB as a whole. Did a 48 way board the other night, low IR with a 3 pole main switch, so went through one by one to identify one circuit which was low. But I remember when I was taught the guy who taught be said not to do that, record low IR for the board as a whole and then call for further investigation to identify any specific circuits.
 
Always good to know how others carry out their work, when doing an EICR would you simply test the IR on a DB as a whole. Did a 48 way board the other night, low IR with a 3 pole main switch, so went through one by one to identify one circuit which was low. But I remember when I was taught the guy who taught be said not to do that, record low IR for the board as a whole and then call for further investigation to identify any specific circuits.
I suppose it depends on different things.
What your quote or allows for.
Agreements made with the client beforehand.
Relationship with the client and what they expect.
Time scales, etc.
If it's not a quite recently installed job, without additions or alterations (in other words, a dream), it would be very unusual to be able to do a successful global IR test on such a board.
 
I suppose it depends on different things.
What your quote or allows for.
Agreements made with the client beforehand.
Relationship with the client and what they expect.
Time scales, etc.
If it's not a quite recently installed job, without additions or alterations (in other words, a dream), it would be very unusual to be able to do a successful global IR test on such a board.
If you could get extra time doing testing, which in my opinion, is part of the job anyway, good luck....but not my way....nor yours, I feel.
 
Rarely do a global IR as I generally work large commercial or industrial sites and from past experience it rarely pans out unless it is a few rudimentary circuits.
 

Reply to Commercial EICR - Your opinion? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
759
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
748

Similar threads

It applies to commercial if it shares the same supply as a dwelling.
Replies
4
Views
546
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
675
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top