Divspark
Hi everyone looking to clarify something, had a tester onsite today testing circuits we've been installing the past few weeks, in his opinion he found fault with one circuit, we had wired a 30m radial circuit in 2.5mm 2core & earth fp200 on a c16 mcb. The cable was clipped direct throughout its entire run so according to the tables it should be rated 27amps, he said all radials feeding sockets should be 4mm and that it was in the regs, don't get me wrong we would normally cable in 4mm but seen as all we had was 2.5 and the table said 27amp we didn't see an issue. So my question is in all reality was he right ? And if so where in the big green book is the reg stateing it ?