Read the first post again it is not that confusing .

The report will state that the 125a sub mains from the 400 amp panel board exceed maximum permissible zs values but the disconnection time will be met by the 80 amp switch fuse at source
This statement to me gives the impression is all okay and maybe it is as fault protection is provided but the issue of selectivity is not clearly addressed. There is no selectivity between x and the supply protective device y whereby fault protection is provided by y. Or something along those lines.
 
This statement to me gives the impression is all okay and maybe it is as fault protection is provided but the issue of selectivity is not clearly addressed. There is no selectivity between x and the supply protective device y whereby fault protection is provided by y. Or something along those lines.

I have commented on the poor discrimination between devices and made them aware of the inconvenience a fault may cause .

cheers lads thanks for your input ....
 
Hi Guys,
in an installation with one main Distribution board and several submain-DBs, do when you measure Zdb on a submain-DB incomer? and do we need to verify the Zdb value with the up stream protection device?( for example, a 125A, MCCB on the MDB outgoing). If yes, how can I get the max Zs values for MCCBs ?
 
Last edited:
Hi Guys,
in an installation with one main Distribution board and several submain-DBs, do when you measure Zdb on a submain-DB incomer? and do we need to verify the Zdb value with the up stream protection device?( for example, a 125A, MCCB on the MDB outgoing). If yes, how can I get the max Zs values for MCCBs ?
Hello Arashabb this is an old thread so you need to create a new one.
 

Reply to Commercial sub mains exceed max zs of mccbs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Recommended Sponsor News

  • Article
thanks for the clarification. ( also thanks to Dan. ).
Replies
6
Views
2K
  • Article
More info on link below http://sbsc.uk.net/
    • Like
2
Replies
22
Views
9K
  • Article
Happy Friday Everyone! Subscribe for more jokes direct to your mailbox or send us your own jokes to be in with a chance of featuring, by clicking...
    • Like
2
Replies
27
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top