Hi Guys
I have some remedial works to do on a site with static caravans. They are all fed in 25 2c swa in radial's supply to supply all circuit protection is fine and the insulation resistance tests between L - N are fine. Problem lays with the armouring the have failed leaving very poor continuity. They can't be re glanded because the are concreted into the floor and too short customer wont pay for re-wire just need the cpc continuity. Was going to trim them back common them together with external earth clamps and 16mm G/Y and take it into box through a stuffing gland, lash loads of self amalgamating tape round it to seal it best possible. Any other ideas looked at raychem kits but the boxes and gland plates are in that bad state I wound end up replacing the lot.
Any other plans bar the obvious 'you need a re-wire it's been rotting for 40 years' and walking away.
Thanks Paul
I have some remedial works to do on a site with static caravans. They are all fed in 25 2c swa in radial's supply to supply all circuit protection is fine and the insulation resistance tests between L - N are fine. Problem lays with the armouring the have failed leaving very poor continuity. They can't be re glanded because the are concreted into the floor and too short customer wont pay for re-wire just need the cpc continuity. Was going to trim them back common them together with external earth clamps and 16mm G/Y and take it into box through a stuffing gland, lash loads of self amalgamating tape round it to seal it best possible. Any other ideas looked at raychem kits but the boxes and gland plates are in that bad state I wound end up replacing the lot.