Yep, if you go to the letter of the regulations I agree. RCBO's are the only way to fully comply with the regulations when installation methods, circuit types and use of installation by ordinary persons has to be followed.
But as we all know, sometimes you have to read between the lines with the regs, and the term "minimising" can be covered by installing two RCD's, with the circuits in the same areas split between the two. A front end RCD with no discrimination further down for no particular reason will not comply with 314.1 (i).
If this is a commercial installation then there may be no specific reason why 30mA protection is needed if cables are not unprotected and buried in walls. If the ring mains only supply comms equipment the I would suggest they were under the control of skilled or instructed persons. Also the fact that IT equipment has high earth leakage currents, I would use another regulation (not got my regs with me at the mo, but I'll look it up) to bypass the requirement for additional protection for the sockets by 30mA RCD anyway...
But as always, everybody has their own interpretation of the regs,