I know that on new installs the glands used on Exe joint boxes must be certified Exe or Exe/Exd glands.
My question is on existing Ex installations prior to 2007 was it permitted to use a CW gland swa gland on armoured cables?

cheers
 
Yes I know the areas were zoned before 2007 but prior to this date uncertified glands were permitted to be used on Exe boxes in zoned areas. My question relates to what constitutes an uncertified gland. Does this mean CW glands were permitted?
 
I'm not well up on the detailed requirements of exe but as a minimum I would suggest to look at the installation instructions of the junction box. If the MI states that appropriately certified glancing is required to maintain the protection concept then there is only one choice.
Regards
Martin.
 
As far as I can remember certified glands had to be used prior to 2007. I would have to have a look to see if I still have my older complex books to be certain, if I still have them
 
Hi,

EExe requires the appropriate EExd or EExe gland and to maintain IP54 with a certified sealing washer. I believe you may be able to use waterproof glands under certain conditions IEC 60079 , but I have never seen or heard of that option being employed.The only type of equipment that can use an uncertified gland is Exn, but it must still meet ingress protection.

Regards.
 
The answer is no it wasn't permitted to use ordinary glands as they would of provided a flame path etc what I ment to say is I was installing exe exe glands back in the late nineties hope that helps I do have my comp ex though I must admit bit rusty in that are not used it for a bit
 
farmelectrics is talking about Exd as he mentions flamepaths
Prior to the revision of the standard in 2007 you were permitted to use a non certified gland on Ex e equipment provided it met I.P. and impact protection to Ex e standard. You could also use and Ex e or an Ex d gland on Ex e equipment too. You could even use a certified barrier or compound gland if you wanted.
 
We were using flameproof SWA glands back in the 80's, in our companies hazardous areas, but then the company i was working for used the American system, that's always been more stringent than the European Ex systems....
 
farmelectrics is talking about Exd as he mentions flamepaths
Prior to the revision of the standard in 2007 you were permitted to use a non certified gland on Ex e equipment provided it met I.P. and impact protection to Ex e standard. You could also use and Ex e or an Ex d gland on Ex e equipment too. You could even use a certified barrier or compound gland if you wanted.

Listener, is a CW gland classed as a non certified gland or did a non certified gland still have Exe or Exd markings on them but not the Atex cert number for example?
 
If I remember from 10 years back, the minimum requirement for 'e' was a E1W gland. Or was that for IS?

It's been a long time since I dabbled in ATEX but I'm due on the course next month and looking forward to learning it all again.
 
Yes Lee you are right. EPLs seem to catch most guys out that have done their compex in the past. You are able to use non certified glands on IS systems depending upon the equipment installed.
 

Reply to Compex Question Exe joint box gland in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
433
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Cheers guys. I was working on the same assumption, but was aware for MF the wagos in wago box were derated 32s, and couldn't find anything to...
Replies
7
Views
269
Ok I’ll try this when I’m down
Replies
4
Views
405

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top