Hi there I have done the refresher course although failed on the ex03r
My question is what’s the minimum gland spec for
IS
Zone 0
Non armoured cable.
Exia
Metal and plastic enclosure
I’m thinking exd stuffer
 
Hi Dingo, for a single item of equipment Exia you may select an A2 compression gland, certified Exe, Exd, or Exde, alternately you are permitted to use an uncertified gland that has an ingress protection of IP66, these are listed in 60079-14 table 10 note a.
If you use a certified Exe A2 gland the equipment must be rated for the IP of the zone, (eg IP66) that applies to the equipment only, the cable gland entries must have an IP washer installed to the cable gland to attain the required IP66 ingress protection. Regards CJ
 
Hi, if anyone requires advice with regard to the Compex training and Compex refresher training courses, I am here to help. (Compex Training instructor / Assessor).

Jackso.
Recently did my two day refresher and failed EX-03 installation board test. Now have to resist Ex-01 and Ex-03. I have Compex course files but any suggestions on information selecting equipment to aid with the re-sit
 
Compex 5 day course presented at Compex centre 051, Scunthorpe H.E.T.A. With ten candidates, very intensive training. The feedback was very positive with three of the candidates remarking that had they realised just how much there was to learn they would have opted to do the two day Compex Foundation course (All theory), and progressed to the 5 day full course at a later date. Their results will be available in 2 to 4 weeks and I will update this page then.
Which centre you from?
Hi Jackso, new member here, looking for some help regarding a query I have on the inspection checklists found in the ex02 and ex04 compex exams? Any help would be much appreciated. Jim
[automerge]1570471348[/automerge]
Hi Jackso, new member here, looking for some help regarding a query I have on the inspection checklists found in the ex02 and ex04 compex exams? Any help would be much appreciated. Jim
Source URL: Industrial - Compex Training Advice Available - https://www.electriciansforums.net/threads/compex-training-advice-available.170720/page-2
 
Jackso.
Recently did my two day refresher and failed EX-03 installation board test. Now have to resist Ex-01 and Ex-03. I have Compex course files but any suggestions on information selecting equipment to aid with the re-sit
Hi, contact me by e-mail at [email protected] and I will provide you with some guidance, regards, CJ
[automerge]1570613789[/automerge]
Jackso.
Recently did my two day refresher and failed EX-03 installation board test. Now have to resist Ex-01 and Ex-03. I have Compex course files but any suggestions on information selecting equipment to aid with the re-sit
Hi, contact me by e-mail at [email protected] and I will provide you with some guidance, regards, CJ
[automerge]1570614127[/automerge]
Hi, what’s the best compEx book to read ?
Hi, I recommend, Hazardous Areas For Technicians, ISBN 978-1-912014-95-8 available from Amazon priced at ÂŁ14.50, comprehensive guide written by a very experienced Compex training instructor/assessor Ian Staff. Regards, CJ
 
Last edited:
Hi timbobelfast, yes, the new refresher format was introduced in 2018. Very intense, one day of refresher training. Very busy second day, all assessment, practical electrical and instrument inspection, identify faults, remedial actions and fault codes, which are considered as important as the actual fault. One hour cable installation assessment. The Ex01-Ex03 board exercise, which is now online, computer based from next Monday 14th Jan 2019. And of course the final online exam which has been reduced from 60 to 50 questions, with the added bonus of an open book exam, the handbook provided by the test centre, to be returned upon completion, regards, Colin, Compex instructor-assessor, centre 051 Scunthorpe.
Colin,
What’s the name of the booklet that lists all the j/boxes etc. that you get with the online installation board, can I find a copy anywhere please?
 
Colin,
What’s the name of the booklet that lists all the j/boxes etc. that you get with the online installation board, can I find a copy anywhere please?
Hi spf3358, unfortunately the booklet for the online installation board exercise Ex01-Ex03 is a controlled documents the property of JTL, the Compex awarding organisation, they cannot be purchased, Regards, CJ
 
Hi Jackso,
Can you advise what the current practical entails? Is there anything I can practice for i.e. are the glands still putty or are they now resin?

Wouldn't mind bashing a few out before going as I don't do much of it at the moment.
Cheers,
Dan
 
Hi Jackso,
Can you advise what the current practical entails? Is there anything I can practice for i.e. are the glands still putty or are they now resin?

Wouldn't mind bashing a few out before going as I don't do much of it at the moment.
Cheers,
Dan
Hi Dan, my advice depends upon which Compex course, the five day or the two day refresher, barrier gland always used resin, barrier gland not required for the refresher, let me know which course and I will provide further advice. Regards, CJ
 
Hi CJ,

Will be taking 01-04. From other guys I know, they said they had to use putty (was a few years back when they did it though) - I would've expected resin as it's obviously better. Haven't made either off for years.

Thanks,
Dan
 
Hi CJ,

Will be taking 01-04. From other guys I know, they said they had to use putty (was a few years back when they did it though) - I would've expected resin as it's obviously better. Haven't made either off for years.

Thanks,
Dan
Hi Dan, Ex01 and EX03 Electrical and instrument installations, I recommend practice at terminating SWA and braided cables, and the barrier gland if you can. Ex02 and Ex04 Electrical and instrument inspections, pay particular attention to the fault codes, they must be accurate and specific to the fault identified. You could identify all of the faults but still fail the assessment if the codes for the visual, close and detailed faults are incorrect. You can find the fault codes in the Toolbox guide EEMUA Publication 214 Edition 7, that is provided on the 5 day Compex course. Revise methods of protection, zones, and equivalent ATEX Categories and international Equipment protection levels, all in the toolbox guide, Regards, CJ.
 
Hi, if anyone requires advice with regard to the Compex training and Compex refresher training courses, I am here to help. (Compex Training instructor / Assessor).
Hi Jack,

i desperatly need any help you can offer towards the compex 1-4 course

i am going to be taking the course in the next month or so i havent got a definite date because its in the hands of my employer so I'm just trying to get ahead as i know its tough

thank you
 

Reply to Compex Training Advice Available in the The Welcome Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
795
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
827

Similar threads

E
  • Article
My son and tiling training. Hi guys. My son, 16, not enjoying school or college has been working with me for a bit of money doing some grouting...
Replies
0
Views
154
Etherglide
E
  • Article
Tiling Courses at UK Pro Tiling Training Hi all Darren here from NETT, Just heard about Diamond and a few other Tiling companies in trouble, I...
Replies
0
Views
244

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top