HI,
I have a difficult to diagnose problem. I've had two qualified electricians try and sort it, but no solution yet.
It is tricky (interesting?) and would love to hear comments/suggestions.
I have a long barn conversion.
Supply enters one end into a CU. There is a 50A 30mA RCBO feeding a 16mm T&E which goes about 50yds to an annex where it terminates in a standard split load CU. (Two 30mA RCDs with assorted MCBs each side).
Because the earth conductor in 16mmT&E is of insufficient size, an earth spike is additionally connected at the annex end.
One MCB supplies a 'pump room' which supplies a bore hole pump and - recently - a variable speed water pressure pump.
Every time the variable speed pump starts it blows the RCBO. (Never the RCD).
But, it is not faulty. If plugged into a regular socket on my main house ring main it works fine.
I have a socket near the main CU also connected to the RCBO - for test purposes.
If the pump is plugged in there it trips the RCBO ONLY IF the annex DB main switch is on, and at least some MCBs are enabled.
The situation is fully reproducible - although putting MCBs on in turn gives inconsistent results.
My personal view is that this is related to the earth spike having a substantially lower inductance to earth for the startup motor current and 30mA is current flowing through some domestic appliance in the annex to the spike. However, this is difficult to argue as the problem occurs when the pump is pugged in at either end of the 50yds 16mm cable.
Supply appears to be TN-C-S (although there are 3 cables coming from the transformer outside).
Any clever ideas?
Peter
PS All Zs etc within spec. 1V shown on test equip between N and E in whole installation!
I have a difficult to diagnose problem. I've had two qualified electricians try and sort it, but no solution yet.
It is tricky (interesting?) and would love to hear comments/suggestions.
I have a long barn conversion.
Supply enters one end into a CU. There is a 50A 30mA RCBO feeding a 16mm T&E which goes about 50yds to an annex where it terminates in a standard split load CU. (Two 30mA RCDs with assorted MCBs each side).
Because the earth conductor in 16mmT&E is of insufficient size, an earth spike is additionally connected at the annex end.
One MCB supplies a 'pump room' which supplies a bore hole pump and - recently - a variable speed water pressure pump.
Every time the variable speed pump starts it blows the RCBO. (Never the RCD).
But, it is not faulty. If plugged into a regular socket on my main house ring main it works fine.
I have a socket near the main CU also connected to the RCBO - for test purposes.
If the pump is plugged in there it trips the RCBO ONLY IF the annex DB main switch is on, and at least some MCBs are enabled.
The situation is fully reproducible - although putting MCBs on in turn gives inconsistent results.
My personal view is that this is related to the earth spike having a substantially lower inductance to earth for the startup motor current and 30mA is current flowing through some domestic appliance in the annex to the spike. However, this is difficult to argue as the problem occurs when the pump is pugged in at either end of the 50yds 16mm cable.
Supply appears to be TN-C-S (although there are 3 cables coming from the transformer outside).
Any clever ideas?
Peter
PS All Zs etc within spec. 1V shown on test equip between N and E in whole installation!