Hi all,
A maintenance friend today asked for a bit of advice. He said cabbles supplying compressor are very warm / hot to touch. (Also thought he could feel them vibrating slightly)
The cable is a swa 25mm and is pulling 55A per phase. I said being a compressor it might have a VFD and might be causing harmonics.
All I wanted to know is because I don't really understand harmonics etc am I wide of the mark and if so what could be causing cables to get hot and who should he call in to look at it.
Thanks again for any info...
 
One VFD will not generate harmonics enough to cause that issue. No at the size it is. An most likely it's not using a neutral anyway.

Remember, cables are rated to operate at 70degC. Has he actually measured the temp, because just touching the cable with a hand isn't good enough.

Also, the hot weather you guys are having currently is bound to play a part into it.
 
What are the measured currents in each line?

http://www.aeicables.co.uk/literature/CurrentRatings.pdf

The volt drop per m for 25mm 3/4 core clipped direct 30C ambient, 90C conductor temperature is 1.65 x 10exp-3 V/A/m
So, Joule heating per m per conductor is volt drop/m x current x current =

1.65 x 10exp-3 x 55 x 55 = 5W/m

or 15W/m for 3 core cable.
 
Last edited:
I am not surprised the cable is warm. Each conductor is surrounded by three layers of plastic insulation and at the moment the ambient air temperature is high 20s maybe more inside the factory. So, conductor temperature will be higher than during periods of cooler ambient air in order produce a temperature gradient between them and surrounding air sufficient to cause a heat flux of 15W/m. Check the temperature rating of the SWA cable.
 
Hi - The 25mm cable is running approx half its rating assuming no harmonic content. If somehow there were harmonics, the highest example of harmonic content given in BBB would see this still being within 25mm capacity, I reckon (42% THD on p380). Perhaps have a look for signs of heat damage near terminations? And then have a cool drink, or at least I will :).
 

Reply to Compressor cables getting warm. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Yet another update: I believe what EDF have done is moved me from an Economy 9 to an Economy 7. I've just emailed them to ask if they can switch...
Replies
2
Views
276
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top