I'm scratching my on this because I've never done it before. I'm on a new build school wire with quite a few computer RFC's using 2.5 T&E + a 4mm single Earth that we are just pulling in now. When it comes to us testing these circuits, how do I/we record the results?
Both the 1.5mm CPC and the 4mm Earth will be in the same terminal at each socket therefore creating a parallel path with a higher resistance if only one of them is tested, but these are going to always be like this, so do I record the combine findings or test for continuity on each of the R2's then record the R2 of each on one cert or make another page for one of the findings?
I've got it in my head that we need to do 3 lots of R2 tests and put them all on paper:-
1.5mm CPC
4mm Earth
Combined CPC + separate Earth.
Or is it just me + the QS + another very qualified spark that is having a blond moment???
Both the 1.5mm CPC and the 4mm Earth will be in the same terminal at each socket therefore creating a parallel path with a higher resistance if only one of them is tested, but these are going to always be like this, so do I record the combine findings or test for continuity on each of the R2's then record the R2 of each on one cert or make another page for one of the findings?
I've got it in my head that we need to do 3 lots of R2 tests and put them all on paper:-
1.5mm CPC
4mm Earth
Combined CPC + separate Earth.
Or is it just me + the QS + another very qualified spark that is having a blond moment???