Discuss Computer RFC Testing??? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Dunno bout anyone else but I'm learning.
Turns out what I was taught wasn't 100% accurate.
Thanks kingeri
Does that mean my last statement (as I was taught) is wrong? I'd ask for a rebate if it was but I didn't pay!!
The 2 cpc's definitely have to be tested as 1. Been thinking about this for a while and if they are joined throughout the circuit they are performing the same function.
My solution would be to connect the 1.5mm CPC's in one of the socket outlets earth terminals, and the 4mm earthing conductors to the other socket earthing terminal!! At the CU/DB connect the 1.5mm CPC's in one termination on the earth bar and the 4mm earthing conductors into a separate termination next to the 1.5mm!!...Sorted!! As this is for IT purposes, the socket outlets will require 2 No's of earthing terminals at the socket outlet accessories (which most do these days).
Sintra I cant be 100% sure that the 4mm earth single is touching the T&E on its entire run so I dont know that I would call it a cpc. Think I've just stated another question???
only 1 reading is to be recorded , and as the 4mm is performing the role of cpc as well as the t&e , then take measurement of both combined would be my solution.